- Reaction score
- 5,382
yes Tel..select protection device according to the cable size. the rating if the device must be less than the current capacity of the cable ( allowing for derating ), e.g. if you have a 2.5mm circuit with a ccc of 23A, you would select a 16A or 20A MCB. on circuits with high start up currents, e,g. motors, you would select a type c or d. then you work out your Zs for the circuit and make sure it's below the max. allowede for the chosen MCB. if it's not, start again.
and Max. Zs for a C curve is half that for a B.....Max. Zs for a D curve is half that for a C....