Replacing 15 year old FAR Italian manifolds (2 downstairs, 1 up) with new Warmup units. However, old actuators have 4 core and new only have 2 core. Can someone please explain what the additional 2 cores are used for in the old actuators and how to modify the wiring for the new, and perhaps if at all possible supply a wiring diagram for an S Plan system with 4 zone valves - 1 for manifolds downstairs, 1 for manifold upstairs, 1 for two towel rails upstairs, 1 for hot water. Many thanks for any help.
 
4 wire actuators incorporate a switch that operates when the actuator is 'on'. This switch will be connected in parallel with the ones on the other actuators, and used to turn the boiler and pump on.
A 2 wire actuator system will have a diode connected to the 'live' wire of each actuator, the second wire from each of the diodes are all connected together and connected to a relay. The contacts of this relay are then used to switch on the pump and boiler.
 
4 wire actuators incorporate a switch that operates when the actuator is 'on'. This switch will be connected in parallel with the ones on the other actuators, and used to turn the boiler and pump on.
A 2 wire actuator system will have a diode connected to the 'live' wire of each actuator, the second wire from each of the diodes are all connected together and connected to a relay. The contacts of this relay are then used to switch on the pump and boiler.
Thank you, thats very helpful.
 
You get similar with 2 port zone valves. Some have just a blue and brown wire (plus sometimes an earth) which operates the valve motor. Some also have grey and orange wires, which connect to a microswitch which operates when the valve is open.
 

Reply to UFH - 4 core old and 2 core new Actuators in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

A combi is heating 5 ufh zones downstairs and 1 radiator zone upstairs. It has a two port valve for each. My question is, would you fit this with...
Replies
4
Views
1K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
998
Hi all, I have a slightly mish-mash heating set up, in that downstairs I have wet underfloor heating with an individual thermostat per room, but...
Replies
1
Views
2K
Hi. I’ve recently had installed a manifold (including zone valve and pump) for the newly installed Wet UFH in my extension. The system is split...
Replies
14
Views
3K
Hello, I am renovating a house. I am rewiring myself. I am getting an electrician to install a new consumer unit & test all my work. I'm looking...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock