Discuss Under floor heating mat 15Amps in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi there
I need your opinion on this one, I need to fix mat 18sqm (200w). Client instead of one mat bought 2 mats (12sqm)+(6sqm) one thermostat . Went through the manual of under floor heating so 12sqm (2400w) + 6sqm(1200w) total 3600w.
Now my question, how do I spur nearly 16amps, standard spur comes up to 13amps. Those 2 mats can be on one thermostat up to 16 amps anything above that need to be on contractor .
Is there any way to get that connected on switch spur? Or the only way is to split those 2 mats add another supply and thermostat for it?
Did you ever had such a situation?
Thanks for any reply.
 
I need your opinion on this one, I need to fix mat 18sqm (200w). Client instead of one mat bought 2 mats (12sqm)+(6sqm) one thermostat . Went through the manual of under floor heating so 12sqm (2400w) + 6sqm(1200w) total 3600w.
I do not understand your maths. The 200watts is per square metre. So the original 18sqm mat would be 3600watts. The mats the client has bought will also be exactly the same at 3600watts.
In both cases you will need a separate circuit, (16amp minimum) and you need to make sure that the thermostat/programmer and any switches are capable of a load of that size.
 
I do not understand your maths. The 200watts is per square metre. So the original 18sqm mat would be 3600watts. The mats the client has bought will also be exactly the same at 3600watts.
In both cases you will need a separate circuit, (16amp minimum) and you need to make sure that the thermostat/programmer and any switches are capable of a load of that size.
Hi maybe I have ask wrong question. I do have dedicated cable for under floor heating and it will be on 20 amp rcbo but the question is you got to have switch spur to isolate it before its power thermostat. How do I do the spur when the load is over 13 Amps? ( double pool isolator 20amp? )
 
Hi maybe I have ask wrong question. I do have dedicated cable for under floor heating and it will be on 20 amp rcbo but the question is you got to have switch spur to isolate it before its power thermostat. How do I do the spur when the load is over 13 Amps? ( double pool isolator 20amp? )
Your dedicated circuit is a radial, so a connection to a radial is just part of the radial, it's often called a branch.
The term "spur" is when a single cable connection is made to a ring final circuit.
It's important terminology as the branch you are making from the radial does not need a fused connection unit (you would if you were spurring from a ring).

You do need to be able to isolate the UFH from the radial so, yes, a 20amp Double pole switch is the way to do it. Current on the radial is limited by the 20A RCBO.
 
Do you have the necessary teat equipment to test this once it is installed?
 

Reply to Under floor heating mat 15Amps in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm after some advice please, I have carbon mat underfloor heating throughout my bungalow, each room has its own thermostat and are fed via a...
Replies
1
Views
791
I have a customer that has 3 heating mats under the tile. This was installed a while back and a relay was used. I measured a 21 amp draw for all...
Replies
4
Views
2K
m having a bit of an issue that is proving difficult to resolve. For 2 years I have been having no problems with my setup. I have a 3 zone house...
Replies
1
Views
1K
Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K
Hi All I’m after some advice, I am doing a restaurant fit out involving a number tables that have hot pots built into the table, for customers to...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock