Currently reading:
Under floor heating over 3kw

Discuss Under floor heating over 3kw in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Sb8389

-
Reaction score
25
Hi guys
Being to a job today where the builder has installed some electric under floor heating
Total area is 20.5 m2
The mats are 150w per m2
The total load is just over 3kw.
He has first fixed the wiring and checking it he has used a socket wired off the ring main to spur off to a switch spur where has then wired a 1mm t&e to the thermostat direct In a dot and dab wall so clipped direct.
I know the CCC of a 1mm refC is around 16amps so well within the limit.
In my opinion i would have recommended it being installed on its own circuit as I know it’s not good practise wiring it off the ring main.
Do you foresee any future issues with the install as I may be overthinking it but don’t want to have issues further down the line as I am making the final connections.

Thanks
 
I am presuming the builder did the design and cable calcs since he did first fix it’s up to him to sign on the cert that he did the design.

He has also done the testing by attaching a plug and plugging it in.

If you want to second fix and notify the work with his details filled in the design and testing boxes fine, But i would walk away from this one.

My concerns:

Over 3KW so over 13amps. Cannot be on a 13A FSU.

Any load 2KW or more should have its own dedicated circuit.

The good old bang test. Switch it on without any testing.

Unless I have seen first fix and been involved in first fix I won’t finish a job. In this case I would like to see the location of thermostat and the underfloor heating mats before being put down so I could clarify the actual load.
[automerge]1569022264[/automerge]
To add to the above I would have probably split it into 2 on separate circuits.

Just had a thought. Is the programmer rated at a maximum load, I think most are.
 
Last edited:
Hi guys
Being to a job today where the builder has installed some electric under floor heating
Total area is 20.5 m2
The mats are 150w per m2
The total load is just over 3kw.
He has first fixed the wiring and checking it he has used a socket wired off the ring main to spur off to a switch spur where has then wired a 1mm t&e to the thermostat direct In a dot and dab wall so clipped direct.
I know the CCC of a 1mm refC is around 16amps so well within the limit.
In my opinion i would have recommended it being installed on its own circuit as I know it’s not good practise wiring it off the ring main.
Do you foresee any future issues with the install as I may be overthinking it but don’t want to have issues further down the line as I am making the final connections.

Thanks
Advisable to supply loads @2KW and above from a dedicated circuit, coming from a spur off an, RFC is not the way to go, bad move call him back and get him to do the job properly.
 
Some of the controllers are rated at 16A so would be ok on a 16A radial
but a 13A FCU isn't. unless you're going to use the 16A MCB for fault protection. overload protection is not required for a fixed load such as this.
 
The stat is rated at 16amp so can carry the load. He has now first fixed all cables so is awkward to see his routes but is pretty self explanatory as his stat is only half a meter from his spur that he’s installed. He has laid the accolade mats he told me so they are 0.5mx6m he has laid 7 of these. Although he did tell two of these he cut to 5m so brings the square meter age down a touch but my calcs still come in at pretty much 13amp.
I did look at the potential for a new circuit but now all plastered and customer does not want disruption. I understand it’s bad design but other than potential to blow the fuse although if he is telling me the truth it would be borderline it’s full capacity. I don’t see any overload issues with the cable size he has used really, is there any other issues I should be mindful off that I have not thought off.
 
The stat is rated at 16amp so can carry the load. He has now first fixed all cables so is awkward to see his routes but is pretty self explanatory as his stat is only half a meter from his spur that he’s installed. He has laid the accolade mats he told me so they are 0.5mx6m he has laid 7 of these. Although he did tell two of these he cut to 5m so brings the square meter age down a touch but my calcs still come in at pretty much 13amp.
I did look at the potential for a new circuit but now all plastered and customer does not want disruption. I understand it’s bad design but other than potential to blow the fuse although if he is telling me the truth it would be borderline it’s full capacity. I don’t see any overload issues with the cable size he has used really, is there any other issues I should be mindful off that I have not thought off.
Sb I think you'd be crazy to sign off this work. A 3kW load on a 1mm cable spurred off a ring, there's not really anything else to say. I would never put my name to that. Try not to feel pressured by the builder. It needs to be on a dedicated circuited 16A MCB with 2.5mm cable (possibly 1.5mm).

The 13A fuse will not blow at 13A it will keep going for ever at 13A, which means that 1mm cable will be constantly (while the heating is on) taking it's full load and that's assuming it's CCC is 13A in the stud wall, it could be less.

It is difficult to say 'no', but sometimes we have to. I don't want to be thinking back over my career worrying if I've installed anything dangerous.
 
The stat is rated at 16amp so can carry the load. He has now first fixed all cables so is awkward to see his routes but is pretty self explanatory as his stat is only half a meter from his spur that he’s installed. He has laid the accolade mats he told me so they are 0.5mx6m he has laid 7 of these. Although he did tell two of these he cut to 5m so brings the square meter age down a touch but my calcs still come in at pretty much 13amp.
I did look at the potential for a new circuit but now all plastered and customer does not want disruption. I understand it’s bad design but other than potential to blow the fuse although if he is telling me the truth it would be borderline it’s full capacity. I don’t see any overload issues with the cable size he has used really, is there any other issues I should be mindful off that I have not thought off.

How has he joined 7 mats together?
How did he cut the mat down? This is not normally possible.
3kW is too much load for an SFCU to handle for the long periods that heating will be on for. There's more to this than straightforward maths, experience shows that an SFCU will burn out because of this.

I would strongly advise that you refuse to connect and advise the end customer that this situation could be dangerous.

The builder has carried out the work so they are responsible for the electrical safety and part P notification etc. Unless you are registered for third party sign off and have been involved with this from the design stage then technically you would be breaking the law to sign it off.
 
I do agree
How has he joined 7 mats together?
How did he cut the mat down? This is not normally possible.
3kW is too much load for an SFCU to handle for the long periods that heating will be on for. There's more to this than straightforward maths, experience shows that an SFCU will burn out because of this.

I would strongly advise that you refuse to connect and advise the end customer that this situation could be dangerous.

The builder has carried out the work so they are responsible for the electrical safety and part P notification etc. Unless you are registered for third party sign off and have been involved with this from the design stage then technically you would be breaking the law to sign it off.
He has laid 7 0.5x6m mats and taken all cables back to a single joint box although he did say he cut a couple mats down to 5m so not 100% on the square meters he, he has then run a 1mm from that point to the stat and a 1mm supply from the switch spur to the stat. I don’t really have any intention of signing it off, im getting hassle now as it would mean quite a bit off mess to install a new supply although I have explained the situation.
 
I do agree

He has laid 7 0.5x6m mats and taken all cables back to a single joint box although he did say he cut a couple mats down to 5m so not 100% on the square meters he, he has then run a 1mm from that point to the stat and a 1mm supply from the switch spur to the stat. I don’t really have any intention of signing it off, im getting hassle now as it would mean quite a bit off mess to install a new supply although I have explained the situation.
As well as not signing it off I’d encourage you not to do anything to the circuit that would implicate you as the last person to work on that circuit.

Don’t be lumbered with liability.

Also write a report on the works undertaken so far, stating it was not you who carried out this work.

A**e covering time.
 
I’m back there on Thursday so going to try and convince them of the potential issues going forward and to install a new circuit, from memory it could be wired in conduit on the outside straight into the garage where the consumer unit is. 2-3 hours work just for peace of mind All round is worth it.
 
Minimum cable CSA for other circuits is 1.5mm unless wired in flex. I’m not at home at the minute so can’t give the reg number.

I would get the builder and customer there at the same time to explain my concerns and solution then let them make a decision.

If signing this off you are taking responsibility for the circuit and the UFH mats, how do you know he hasn’t damaged them on installation? Wouldn’t be the first time someone has been blamed for damaged UFH.

Unless I knew the builder well I wouldn’t be signing it off.
 
... he did say he cut a couple mats down ...
As Davesparks says, with some (many, most ?) systems, you cannot cut them down - and where you can, it may need special measures to maintain the integrity of the element.
Some "mats" are simply a wire system that's pre-laid out on a plastic mesh to make it easier to install. Some heater cables have multiple heating elements which can be cut in certain places. Others cannot be cut as the L&N wires are the elements, and are joined together at the far end - if you cut it then you need to re-join them and the resistance will be lower and the W/m higher than designed for.
So this alone should ring alarm bells. Make sure that you document everything that you were not involved in so they can't come back to you if there's any problems.
 
Maybe show the customer some of the comments on this thread.
 
How come you are concerned with what the builder has done.
Because he may not be as self assured as you are Westward. He probably has a working relationship with the builder and feels he has to tread lightly. Even though my builder is a friend there are still times when i think 'should I or should I not put my foot down on this point'. Having said that, this is one time I would definitely be putting my foot down.
 
this is one time I would definitely be putting my foot down.

hopefully not too hard on the UFH mat. :( :( :(
 
1.5mm is the minimum for a power circuit. It's in the regs somehwere. 1.0mm is only acceptable for lighting circuits. Really should have it's own circuit also. Definately can't sign this off. What do you think the nic/napit inspector would say?
What’s the definition of a power circuit?

surely all circuits are power circuits. I know I’m being pedantic, but I see nothing wrong with using 1 mm for a dedicated circuit that needs minimal power. Cheaper and better for environment.

i agree a spur from a socket circuit minimum is 1.5mm whether ring or radial as long as it is fused down as per regs and it’s what I do,

but in theory 1mm fused down spur from a ring or radial socket, I see nothing wrong with that.
 
If you look at table 52.3 it also depends on the type and material used for the construction of the cable.
 
Just an aside - I've only ever been involved with UFH once so am by no means expert, but I seem to remember the installation instructions for my example demanding IR tests to be done before the mats are fitted, once they're laid down and again after the floorcovering is installed to keep an eye on the condition of the mats throughout the installaton process. Certainly the one I used provided an area for these results to be noted and suggested it to be left by the CU (apologies can't remember the make). But with this in mind, i'd be concerned about an installation I hadn't been fully involved in
 
Not just IR, resistance as well. Both should stay stable - you really need to detect faults before the floor goes down on top (especially tiles !)
IIRC, my mate's system came from Topps Tiles and the "one free repair" offer was conditional on having taken these measurements.
 

Reply to Under floor heating over 3kw in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top