Hi, hope somebody can help. I am currently wiring a new wet underfloor heating system for builder. The plumber has fitted a 2 port valve and the pump that is part of the manifold.
The existing system is a y plan.
I was going to leave existing system how it is and fit a wireless programmable stat to underfloor heating. To keep it separate I was going to fit a contactor to the switch live to the boiler
Ie from switch live of existing y plan to first A1 of 2 pole contactor and switch live from underfloor heating to 2nd A1 of contactor. This way both systems are kept seperate.
Could anybody with more experience tell me if this would work or better still another way it could be done. Thanks again
 
It wont work as a Y-plan with an additional 2 port valve as the three port will always be open in one position so when the UFH is calling it will start to heat what ever side is open as well. You need 3 x two ports , hot water, radiators and UFH.
 
It wont work as a Y-plan with an additional 2 port valve as the three port will always be open in one position so when the UFH is calling it will start to heat what ever side is open as well. You need 3 x two ports , hot water, radiators and UFH.
That makes sense now you've pointed out because obviously if underfloor is calling either the rads or hot water will be getting hot water flow from boiler. I will have to inform plumber. Thanks
 
With 3 x two ports it just gets wired as an S-plan + with the additional UFH pump


http://ww2.justanswer.com/uploads/PL/PlumbersMate/2014-09-30_082503_splanplusaddingazone3.png

The UFH pump should ideally be connected to the orange of the UFH valve through a relay so its not triggered by the other oranges from the other two valves. Some drawings show it connected to the brown of the valve but this is a bit of a bodge as the valve hasn't actually fully opened.
 
Could anybody explain how it would be wired or what switches what with 3x 2 port valves. Would it be wired as s plan on existing and switch the switch live to boiler through contactor as I said in first post. Thanks
 
What I have found is the boiler is a good distance from the controls and the control box, pump and 3 port valve are in the loft. A bit of a shoddy install to be honest.
Surelly all 3 oranges of valves will go to sw live at boiler. Or are you saying there could be an internal pump in boiler as well.Sorry only I haven't done a lot of heating wiring. Thanks
 
You have the main pump and UFH pump. you only want the main pump to run when either the radiators or hot water or both are calling for heat. If the UFH is calling for heat you want the main pump and UFH manifold pump to run. To achieve this the best way is for the oranges to connect to the sw live in boiler but the orange of the UFH valve to trigger the coil on the relay which closes and fires the boiler when the UFH is calling. The UFH pump will connect to the coil with the UFH valve orange this way the UFH pump doesn't run when either the hot water or radiator valve oranges become live. The bodge way with out using a relay is to connect the UFH pump with the brown of the UFH valve.
 
You have the main pump and UFH pump. you only want the main pump to run when either the radiators or hot water or both are calling for heat. If the UFH is calling for heat you want the main pump and UFH manifold pump to run. To achieve this the best way is for the oranges to connect to the sw live in boiler but the orange of the UFH valve to trigger the coil on the relay which closes and fires the boiler when the UFH is calling. The UFH pump will connect to the coil with the UFH valve orange this way the UFH pump doesn't run when either the hot water or radiator valve oranges become live. The bodge way with out using a relay is to connect the UFH pump with the brown of the UFH valve.
Hi Lee, not sure how to message you.
Boiler is worcester greenstar 11 HE 12/22 (no overun I don't think)
I understand what your saying and how to switch ufh pump with brown of valve( pumping against dead end until valve is open). Could you explain where to get and how to wire a relay in instead. Probably simple when you explain. Thanks for your time and patience. I have enclosed a crude picture...

20161216_205756_HDR.jpg
 
If you are altering this to an S Plan, you need to make sure you have an auto bypass installed. There may already be one but I thought I'd mention it, it should have one anyway really but not everyone installed them on a Y plan
 

Reply to Underfloor heating help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
690
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
Up until now I have steered clear of heating systems. I now have quite a bit of work with a builder and will be expected to deal with the...
Replies
4
Views
872
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
643
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock