Discuss Unexpected / Strange Voltage in the UK Electrical Forum area at ElectriciansForums.net

O

OldTaffy

Hi

Been wiring in a Jacuzzi at a customers.

Wired it to a DP Fused connector unit (to isolate), then to switch junction box.
Switch wire goes to a single pole on/off switch outside the bathroom
The Switched live from Junction box goes to Jacuzzi.

I tested it ALL OK. IR test was +299. RCD Fine. Continuity all fine.

After the tests I still had my Megger attached to the Jacuzzi L + N on Voltage scale.
I noticed that the Megger was reading 180V even though the switch outside the bathroom was OFF.

So I checked FCU, Junction Box, Consumer Unit and switch wiring - Couldn't find anything.

Is this an Inducted 'voltage', that will dissipate?
It does disappear if the FCu is turned off.

Also the Switch cable does run along side 3 other cables and the shower cable too for a short while.
Turning off the shower at the pullswitch didn't make the voltage disappear.

Only things I can think of are -
- Inducted Voltage ?
- Faulty Switch ?
- I've wired the Switch and Jacuzzi the wrong way (Pretty sure I've not, but need to test)

Fast answers appreciated as the customer is already a bit miffed over a couple of other unrelated issues
 
I like the residue theory better, it could have stuck some of the voltage in there permanently ........ sorry being stupid on a Fri morning but 180V does seems to be a high voltage to induce!!
 
Hi

Been wiring in a Jacuzzi at a customers.

Wired it to a DP Fused connector unit (to isolate), then to switch junction box.
Switch wire goes to a single pole on/off switch outside the bathroom
The Switched live from Junction box goes to Jacuzzi.

I tested it ALL OK. IR test was +299. RCD Fine. Continuity all fine.

After the tests I still had my Megger attached to the Jacuzzi L + N on Voltage scale.
I noticed that the Megger was reading 180V even though the switch outside the bathroom was OFF.

So I checked FCU, Junction Box, Consumer Unit and switch wiring - Couldn't find anything.

Is this an Inducted 'voltage', that will dissipate?
It does disappear if the FCu is turned off.

Also the Switch cable does run along side 3 other cables and the shower cable too for a short while.
Turning off the shower at the pullswitch didn't make the voltage disappear.

Only things I can think of are -
- Inducted Voltage ?
- Faulty Switch ?
- I've wired the Switch and Jacuzzi the wrong way (Pretty sure I've not, but need to test)

Fast answers appreciated as the customer is already a bit miffed over a couple of other unrelated issues

Hum, so you'll have S/L and P/L in "your" install - are you sure that you have them correctly connected?
 
The line conductor should theoretically be non referenced so any voltage measurement would be suspect. wire an incandescent lamp across line and neutral, see if it glows at all and measure the VD across the lamp, should then be zero. If not then check for wiring faults.
 
All sorted now -Thanks for idea's

FCU was mis-wired, teach me to forget my specs.

So now the 180v has disappeared. All tests ok now

Thanks
 
Glad you found it. Would I be right in guessing that the FCU has a neon and the supply and load side of either line or neutral but not both was reversed, so that the neon bridged from supply to load and ended up in series with your MFT? Otherwise presumably you would have discovered during testing that a single-pole switch was in the neutral. Just interested to know...
 
Glad you found it. Would I be right in guessing that the FCU has a neon and the supply and load side of either line or neutral but not both was reversed, so that the neon bridged from supply to load and ended up in series with your MFT? Otherwise presumably you would have discovered during testing that a single-pole switch was in the neutral. Just interested to know...
and then there was a deathly silence...
 

Reply to Unexpected / Strange Voltage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
340
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
879
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
570
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
753

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock