Search for tools and product advice,

Discuss Unsatisfactory EICR - 'No RCD Protection', 'CCU not AM3 compliant', 'Water Bond not Attached' in the The Welcome Forum area at ElectriciansForums.net

cherry81

DIY
Reaction score
1
Hi, I have an Unsatisfactory EICR with the following observations (full report attached, with key details blanked) - the apartment block was built in 1995 and there was some rewiring in 2010 - are these genuine reasons to fail the EICR? Contacted the inspector who quoted £695 for remedial work and a 5 year satisfactory certificate (which set alarm bells ringing). Thanks for any advice - I'm happy to proceed, but not knowing anything about this, I wanted to check here first.

1 No RCD Protection - Socket outlets C2
2 No RCD Protection special location C2
3 No RCD Protection - cables burried in walls C3
4 CCU not AM3 Compliant (Plastic Consumer unit) C3
5 No heat detector installed in kitchen N/A
6 Water bond not attached C2
 

Attachments

  • EICR.pdf
    84.2 KB · Views: 77
Last edited:
looks about right to me. those codes are exactly what i would give . if it's rented accommodation, 5 years or change of tenancy is stipulated.
 
1 No RCD Protection - Socket outlets C2 Is this a ground floor flat with potential for powering equipment outside?
2 No RCD Protection special location C2
3 No RCD Protection - cables burried in walls C3
4 CCU not AM3 Compliant (Plastic Consumer unit) C3
5 No heat detector installed in kitchen N/A
6 Water bond not attached C2

All the above seem reasonable, my comment in red on number 1.

What does his quote include, new CU etc?
 
I'd still C2 any socket circuit without RCD protection, metal knives in toasters etc.
 
Thanks for the quick replies!

Here's the details of the quote (he came back with a slightly lower price):
We could not install a heat detector and that just a recommendation but we would still need to change the consumer unit to give the rcd protection this we can do for £600 including a 5 year satisfactory certificate

Sounds like you guys think this is reasonable? really appreciate you looking at it

PS: 2nd floor flat
 
It all looks pretty reasonable. The only possible debate is around the C2 for socket outlets on a flat that isn't ground floor. Ultimately it's down to the inspector who is there at the time.
 
i worry about you, buzz. your posts are getting more sensible by the day. are you on the change? no smileys available .
 
Interesting that the inspection schedules tick everything Coded as satisfactory.
I thought that also
He has
3.7 ticked but there is no effective water bond
4.4 is ticked- yet plastic consumer unit (C3 if OK and no signs of thermal damage)
4.10 is ticked did he add a 6 monthly notice?
4.19 is ticked yet RCD's are present on one circuit in the consumer unit
5.2 is ticked (does he have x ray vision to see all the cable routes below floors / behind walls?)
5.12.1 -5.12.3- he has picked this as a C2 yet has ticked it as satisfactory outcome ???
5.12.5 - bathroom lights not RCD protected but ticked to say OK

Pretty poor standard of EICR report (still an unsatisfactory IMO)
 
I thought that also
He has
3.7 ticked but there is no effective water bond
4.4 is ticked- yet plastic consumer unit (C3 if OK and no signs of thermal damage)
4.10 is ticked did he add a 6 monthly notice?
4.19 is ticked yet RCD's are present on one circuit in the consumer unit
5.2 is ticked (does he have x ray vision to see all the cable routes below floors / behind walls?)
5.12.1 -5.12.3- he has picked this as a C2 yet has ticked it as satisfactory outcome ???
5.12.5 - bathroom lights not RCD protected but ticked to say OK

Pretty poor standard of EICR report (still an unsatisfactory IMO)
It was the 60kVA demand that I noticed - 260ish Amps!

Looks like an older version of Easycert, which is what I use, so just the wrong dropdown chosen, but still shows that it wasn't checked over that carefully.

And clearly some of the tick boxes are incorrectly ticked.

Does make me wonder if the water bond was tested for, or just not visible. Most flats are bonded somewhere (or run in plastic). They weren't visible at the pipework in the flat I checked yesterday (though cables were in consumer unit) but a test verified they were effectively bonded.

Also, according to the test schedule, there doesn't appear to be a lighting circuit?

Did they specify what the special location was that lacked RCD protection? If supplementary bonding was in place (3.8 on schedule is ticked) then lack of RCD protection to lights needn't be a C2

Likewise for appliance sockets on a 2nd floor flat I think C2 is harsh, but of course there may be other factors involved.

The issue is that the engineering judgement of the inspector may be perfectly valid and reasonable - but the EICR doesn't really reflect that.

The price quoted doesn't seem too bad for a board change and other remedial work, but I would enquire what it includes. At that price I'd hope it would be type A RCBOs with Surge Protection, not a dual RCD board with type AC RCDs from Screwfix.
 

Reply to Unsatisfactory EICR - 'No RCD Protection', 'CCU not AM3 compliant', 'Water Bond not Attached' in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
7K
I am a landlord and my managing estate agent just recently organised an electrician to carry out EICR. Came back as unsatisfactory, no RCD...
Replies
27
Views
8K
Hi all, have just ordered my first EICR ever for a studio to 1-bed conversion flat in London. It cost a little less than £80 and the electrician...
Replies
51
Views
8K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock