When installing a new circuit for a pv system it is neccessary to fill in an installation cert. If the earthing can not be verified is it then neccessary to install new 10mm earth wires to gas and water mains or ok to note it on the sheet? Iv'e been replacing earths up to now but this job is sometimes more time taking than the installation itself. What do you guys do?
A long lead can verify if it's within.05 of an ohm but is that good enough?
 
Yes, an EIC is required for a new circuit, along with a schedule of items inspection and schedule of test results.

131.8 - Additions and alterations to an installation
No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate.


Gas and water pipework could read as low as 0.05 ohms between your testing point and the MET due to connections at the boiler.
 

Reply to upgrading of earthing. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
892
Shop with no earth coming from head, overhead lines in sight everywhere - definitely no earth from the DNO. Two 10mm earths going into the DB...
Replies
13
Views
2K
I know PV installers sometimes use SWA to carry DC into the house especially when the PV is ground mounted. Can anyone help me understand the...
Replies
10
Views
3K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
598
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock