Upgrading sub panel in shop to QO816L100DF but existing neutral feed is too short to reach neutral bar. How do I relocate neutral bar?
Just splice the neutral long enough to get to the neutral bar. If it’s outside the panel it must be spliced in an approved box and water tight
 
Just splice the neutral long enough to get to the neutral bar. If it’s outside the panel it must be spliced in an approved box and water tight
Yes - splicing is one option and yes the #4 aluminum neutral would have to enter the bottom of the new panel, then exit into a correct sized j-box, then back into the sub panel. Any splice inside the sub panel is out of the question due to space limitations. The new sub panel is flush mount since the shop is insulated, heated and weather/water tight - my second home. So why a watertight j-box?
 
Why would you have to exit and re-enter the panel again, crimp an inline lug onto the N and heat-shrink sleeve it, it takes up next to no room at all, maybe a few mm wider circumference on the joint itself.
 
Just splice the neutral long enough to get to the neutral bar. If it’s outside the panel it must be spliced in an approved box and water tight
You stated that the neutral is not long enough to make it to the panel. Having said that and your using aluminum wire you will need a 6x6x4 inch junction box approved for outdoor use.
 

Reply to Upgrading sub panel in shop to QO816L100DF but existing neutral feed is too short to reach neutral bar. How do I relocate neutral bar? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have an older Crouse Hinds board with a 200A service. Due to recent rehab on the house, I found I have the need to install a sub panel. I...
Replies
1
Views
1K
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
838
Hello! My shop is currently on a single 15 amp circuit. Is like to upgrade it at the main home panel to a 30 amp. Do I just need to run 10 gauge...
Replies
1
Views
651
Hi, I have been tasked with a kitchen rewire. The current DB is fed by a 16mm armoured. There is a split load old contactum DB which I don’t...
Replies
4
Views
1K
I currently have a 100 amp service that feeds a 100 amp main panel. That then feeds a 75 amp sub panel in the old shop. Then that 75 amp panel...
Replies
1
Views
773

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock