Discuss UPS connection common neutral supply & load in the UK Electrical Forum area at ElectriciansForums.net

H

howsitgoing

Hi

Maybe im over thinking this but need to connect a UPS system to a control panel, the problem is the ccts i want to connect to the UPS are split & all the neutrals are all connected to a single busbar connection unit at the moment which is all normal, but i need to connect a UPS to power supply to 50% off the ccts (PLC ccts only) so can i common up the UPS supply side & Neutral side of this UPS back to the existing busbar connection unit or do i have to split the neutrals & connect them all to the load side only of the UPS.

cheers
baz
 
What sort of loading are you trying to keep energised? how big KVA is the UPs you intend to use?
You may have consider having some sort of load shedding arrangements installed, so as in the event of the power outage only the essential loads are kept going.
 
I'm not sure I've entirely followed your post.
But I think what you want to know is that multiple circuits fed via a ups would need the ups to be upstream of the distribution board which feeds the circuits. Or in other words you would have a distribution board after the ups which feeds these circuits.
 
It's difficult to help when more information is required, I asked you for info in post 3
 
Generally you must not connect supply and load together, because of the increased risk of the supply being back-fed if a fault occurs on the load side. You would have to provide a separate neutral bar for the circuits being moved over to the load side of the UPS.
 
Generally you must not connect supply and load together, because of the increased risk of the supply being back-fed if a fault occurs on the load side. You would have to provide a separate neutral bar for the circuits being moved over to the load side of the UPS.



Lucien, would the best option be to use two Distribution boards, one with the essential circuits, and one for the non essential circuits?

Take a feed from the raw mains, and a feed fom the output of the UPs have two outputs 1 essential and 1 non essential inputs and outputs through a suitably sized contactor 2 NO and 2 NC sets of contacts the control circuit could be either fed fro the raw mains or the UPs output, just depends on how the ins and outs are configured in the contactor, I tried to get sizes and load information from the original poster but he has either lost interest, or been busy working and has no contact with the forum.
 
Last edited:

Reply to UPS connection common neutral supply & load in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
346
I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
562
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock