Discuss UPS on light circuits in the UK Electrical Forum area at ElectriciansForums.net

it would be better if you routed all the circuits through another board otherwise it wont comply.

it will be no differnet than linking a genny to the grids neutrel and earth

How would it not comply? Surely if it is labelled accordingly it would be ok?

I was just thinking, I wouldn't need to link the neutral to the supply neutral, I could just disconnect the neutrals from the main neutral bar and put them into to their own isolated neutral bar that only goes via the UPS.

The earth I would still connect to the main bar though.
 
How would it not comply? Surely if it is labelled accordingly it would be ok?

I was just thinking, I wouldn't need to link the neutral to the supply neutral, I could just disconnect the neutrals from the main neutral bar and put them into to their own isolated neutral bar that only goes via the UPS.

The earth I would still connect to the main bar though.

The plan is getting better, but covering it in labels won't achieve anything.
 
Maybe I should just put an expansion board on the bottom with the light circuits in with the supply to it from the UPS, that way it's all separate.

do you think that would be better?

i know you say it wouldn't comply the other way, can you point me in the direction of a reg to look at as I'm not sure I can find one as I feel it seems possibly wrong but don't think it is.

i can't see that having in the same board would be a problem but would probably be better in a separate enclosure I suppose.
 
How would it not comply? Surely if it is labelled accordingly it would be ok?

I was just thinking, I wouldn't need to link the neutral to the supply neutral, I could just disconnect the neutrals from the main neutral bar and put them into to their own isolated neutral bar that only goes via the UPS.

The earth I would still connect to the main bar though.

This is a more sensible Idea, but ideally Shankys separate board idea is the way I would do it with the UPS primary supplied from a way in your existing board , with totally separate N and E bars for the UPS supplied circuits

Depending on the UPS they run in at least two different modes, some of the better ones have three modes.

Mode 1 is just in bypass while everything is healthy, Line + Neutral (*leaving the E for the moment)
Mode 2 in UPS mode, when the primary supply has failed, depending on how the UPS is configured, this output can be totally isolated from the incoming supply (both L + N), now to the E, * depending on the type of UPS if it is of the totally isolated type it can switch the out going CPC onto one side of the now fully floating side (ie. the designated out going N) making a pseudo TNC-S (CNE link) system on the output side only, this is to maintain the protective measure of ADS.
As you can see during power failure if you joined the incoming N (main side N) to the out going N (and like wise incoming and out going CPCs) you would be creating a N-E short on the outgoing side of your now dead main DB, and also still be partially connected to the grid which is against regulations when using a backup supply.

Mode 3, some computer type UPS have a so called "brown out" mode or "power clean up mode", this mode is less clear cut, and not all makers will divulge fully how they implement this mode being a "propriety" technology aka selling point, types with this facilities are less suitable for what you have in mind.
 
I sorted out a bit of a shambles left by some mob with ups supplies for commercial led strips.
i think it was about 300va load each
schneider made the ups which were large and considerably heavy
there were 2 Spurs one for the supply and one for the output if I remember correctly.
the units themselves were about 600mmx300mm
they seem to work similar to an inverter drive with AC in rectified to a DC bus line and then turned into a nice smooth AC out the other end
the led strips were fed through a dmx board with relays and the like but I've no idea how it was programmed .
i think your idea should work but you will be surprised of the size and cost of a decent ups
 
Spark 68, thank you for this, very informative.

May e putting an expansion board on with the RCBOs for the circuits fed from the ups with its own neutral and earth would be best. That way i know it's separate and will be ok.

The other way is easier but equally this way sounds better and more sensible.

Ill have a look into the UPS supplies and find a suitable one, I don't need a massively powerful one as it's only for lights which are all LED and like now for example only using 36w on one circuit and about 15w on another...

I wonder if I could put a manual change over switch in it too so that I can override the UPS should it go faulty.
 

Reply to UPS on light circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
2K
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
656
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
677
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
544

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock