Discuss Upstairs and downstairs MCBs connected? in the UK Electrical Forum area at ElectriciansForums.net

Eddans

DIY
Reaction score
1
Hi all new here and wondering if you have seen heard of this situation/problem?

I wanted to remove surface mount sockets from the living room wall to decorate. In my old house I would just flick the mcb off for the downstairs ring and then made sure the sockets were dead before proceeding. However in our new house I done the same and flicked the downstairs mcb off only to find that the sockets were still showing 240v, I went back to the consumer unit to check that I had switched off the the correct mcb for downstairs which I had. Out of curiosity I switched the upstairs ring mcb off as well and found that the all sockets were dead upstairs and downstairs. same happens if I turn upstairs off and leave downstairs on both rings are still live. Any thoughts please as it just don't seem right.
Many thanks
 
It isn't right and sound like they have interconnected the rings.

Could be a simple mistake in the consumer unit (fuse box). An could possibly be fixed and tested by an electrician in less than 30min.

It could on the other hand be interconnected in a hidden junction box somewhere and be a pig to find. Unfortunatly no way of knowing until its being tested.

However, this work to rectify it is beyond DIY work.

You need to call an electrician in.
 
sounds like the L for the landing light is taken from downstairs circuit. common back in '60's. not allowed these days.
 
This is not right.
You have either got an interconnected pair of rings or, the connections in the distribution board are incorrect.
You should get an electrician in to sort, could be some strange DIY wiring hiding in there or a simple fix.

Without the right knowledge and test equipment it will be very hard for you to sort this yourself.

P.s. telectrix, re read the first post. This is socket Rfc x2 not lighting circuits.
 
Last edited:
I would imagine the legs of each ring have been crossed at some point or another, either by mistake or stupidity. If you were to test, I would expect to see each MCB has one leg of each circuit. It's not really something you want to be messing around with unless you know what you're doing and have suitable test equipment. Call a local electrician to take a look.

I presume there is no RCD protection on the circuits?
 
Didn't expect such fast responses cheers!

CenterSparks there is 1 RCD covering 7 mcbs. I had a quick look and there are 2 lives in the upstairs mcb and 2 in downstairs mcb
 
This is not right.
You have either got an interconnected pair of rings or, the connections in the distribution board are incorrect.
You should get an electrician in to sort, could be some strange DIY wiring hiding in there or a simple fix.

Without the right knowledge and test equipment it will be very hard for you to sort this yourself.

P.s. telectrix, re read the first post. This is socket Rfc x2 not lighting circuits.

OOPs. I need to stand in the naughty corner for misreading OP.
 
Sure it’s not one half of house (ground floor & first floor) on one ring, other half on another?
Hi all, thanks for the replies, just to update..electrician said consumer unit is wired fine so must be linked under floorboards somewhere and could take a few days to find, which will obviously be £££. As there is new carpet etc its off the cards at the moment
 
Hi all, thanks for the replies, just to update..electrician said consumer unit is wired fine so must be linked under floorboards somewhere and could take a few days to find, which will obviously be £££. As there is new carpet etc its off the cards at the moment

A few days?
I would hope to have a fair idea of what is going on after a few hours of testing using a wander lead and taking all the socket faces off.
anybody on here that agrees with that statement and is in Essex?
 
A few days?
I would hope to have a fair idea of what is going on after a few hours of testing using a wander lead and taking all the socket faces off.
anybody on here that agrees with that statement and is in Essex?
yep half a day should be enough.
 
Hi all, thanks for the replies, just to update..electrician said consumer unit is wired fine so must be linked under floorboards somewhere and could take a few days to find, which will obviously be £££. As there is new carpet etc its off the cards at the moment

What have they done temporarily to make this situation safe?
 
Hi All, better news... the 1st electrician charged £75 for checking the wiring of the 2 MCBs and then wanted a few days to find the problem and more £££. I told another electrician who said No charge if I don't find anything within 1 hour..lol I thought. Anyway he wanted to just have a look at all the sockets in the house at first, he then switched off the MCBs in question and went back to a blanked off socket in the kitchen with tester in hand and bugger me he found a block with 2 cables connected, disconnected them and found that MCB1 is upstairs/downstairs and MCB2
is kitchen and down stairs bathroom. He made both cables safe and said he as seen it loads of times and only charged me £45 but did say that all could do with updated consumer unit and wiring. At least the 2 circuits are now separated and should be safer. I suppose most of you have seen this too?
[automerge]1569253826[/automerge]
davesparks...I forgot to mention that nothing was done by the first electrician to make things safe, he just left..
 

Reply to Upstairs and downstairs MCBs connected? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I bought a new build and noticed the upstairs MCB is controlling some sockets on the opposite floor, so if I flick the upstairs MCB it's...
Replies
31
Views
2K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Good evening all, So been to an upstairs flat today I East ham, the entire road is terraced 2 storey building which look like a row of terraced...
Replies
9
Views
1K
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
850
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
737

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock