Search for tools and product advice,

Discuss Upstairs lighting gone off. in the UK Electrical Forum area at ElectriciansForums.net

M1kbee

DIY
Reaction score
4
All of my upstairs lights have stopped working.

All of the plug sockets both up and downstairs are working and the downstairs lights are fine.

The consumer unit seems to take what look like cartridges roughly 1" x 2.5" / 25mm x 65mm with coloured dots on them.
White - 5amp
Blue - 15amp
Red - 30amp

Anyone got any ideas what's going on?
 
Have you checked both fuses are intact, the 2 white fuses would suggest upstairs and downstairs lighting circuits

Replacement fuse Wylex 5A Cartridge Fuse - https://www.NoLinkingToThis/p/wylex-5a-cartridge-fuse/63771
There's the thing, the fuses don't look like that (unless I'm being a tool and that's what's inside those plug in boxes).
 
You can try swapping the two 5A fuses. If it was a one-off fault like a failing lamp you will find the upstairs work and downstairs no longer. If the fault is still present then unfortunately you will have no lights and two blown fuses!

EDIT Make very sure the power is switched off before you remove or insert any fuses!
 
If there is no change then probably a wiring fault needing professional help.

If it is one-off due to a failed lamp, etc, then just a new fuse like @UNG has pointed you to.
 
Have you checked both fuses are intact, the 2 white fuses would suggest upstairs and downstairs lighting circuits

Replacement fuse Wylex 5A Cartridge Fuse - https://www.NoLinkingToThis/p/wylex-5a-cartridge-fuse/63771
Let us know!

A photo can help if any more questions on what you need.

Again, make sure you switch the main power switch off BEFORE changing fuses.
20220418_164151.jpg
 
As above, there should be a length of fine fuse wire linking the two brass pins, going through the ceramic middle section.

If the fuse has blown that wire will be missing (or maybe two halves with ends showing solidified molten metal). Replacement is fairly easy if you have the correct wire (you can usually buy cards with 5/15/30A wire on them) and a small flat-blade screwdriver to loosen the screws that hold the wire in place.
 
PS, once you've sorted out your blown fuses, afraid to say a new fuseboard upgrade might be recommended. Just saying
Or the plug-in Wylex breakers instead of the fuses as a least-worst option if a new CU (consumer unit = fuse box) is unaffordable.

No, they are not as good as a new board with RCD/RCBO, and the possibility of the new CU coming with other faults being fixed, but they sure beat having to change wire in the dark, working out which one has gone, or the risk of inserting a fuse on the a live fault.
 
We have not long since moved in so there's a few things that need doing.

The lack of lighting became a priority when it went out.

I remembered on my way out that it's a bank holiday and most places are shut.
I'll try tomorrow.
 
Let us know how you get on.

If you need professional help then some member on this forum might be local and able to do so. Don't post personal information, just an approximate address (e.g. town or postcode) and then if anyone here can resound they can get in touch via a private message, etc,.
 
Before you go off buying fuse wire you need to establish if it has actually ruptured.
True, but unless they are about to replace the board it would be a very good thing to have sitting around in case it is needed later (considering the low cost)!

Two quid from B&Q
 
Welcome to the forum mate.
Let us know how you get on.

If you need professional help then some member on this forum might be local and able to do so. Don't post personal information, just an approximate address (e.g. town or postcode) and then if anyone here can resound they can get in touch via a private message, etc,.

The OPs info says he's from Warrington.
 

Reply to Upstairs lighting gone off. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
916
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
609
Hi All, I am currently in the process of building an extension and I need to purchase some led downlights for my kitchen but unsure how many I...
Replies
4
Views
337
This is a strange one, my neighbour is a bit mad, he had a largish extension built in about 2015, the builder attempted to do everything including...
Replies
3
Views
999
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
281

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock