Search the forum,

Discuss Use of sy cable in the UK Electrical Forum area at ElectriciansForums.net

polo1

-
Arms
Reaction score
633
Peeps,
Your thoughts please on the use of sy cable in a domestic setting.
Came across an installation today where the supply to an immersion element had been run in sy cable. Overcurrent protection correct and circuit is covered by a 30mA rcd.

I think we are going to be doing an EICR in the property in the next few weeks and couldn’t decide how this might be coded.

What do you think?
TIA
 
It does not comply with BS7671
20190723_195312.jpg
 
C3 for me as not a suitable cable as this is not its intended use. Also as this is near s heat source the plastic coating will become brittle and crack over time.
 
IMO the braiding must be earthed but not used as an earth! I don't know its capability of carrying the fault current as not enough information has been provided.
Why are you earthing it. No it can't be used as a cpc but connecting it to earth leaves the possibility it could be subjected to fault current and if this is the case you must be satisfied it can carry the fault current.
 
I went to a farm with all the out buildings wired in SY not so long ago. Apparently done by a full NIC contractor. I didn't bother to argue with the farmer but it was rubbish none of the screens were earthed just cut off and taped up through stuffing glands.
What a waste of time and money when there are much better spec cables that can be used!
 
I went to a farm with all the out buildings wired in SY not so long ago. Apparently done by a full NIC contractor. I didn't bother to argue with the farmer but it was rubbish none of the screens were earthed just cut off and taped up through stuffing glands.
What a waste of time and money when there are much better spec cables that can be used!

You would be amazed by the amount of ‘electricians’ who just cut off the braiding
 
I really dislike sy cable for anything other than maybe industrial machine wiring, I come across it as a maintenance spark all the time and see mechanically biased engineers installing final circuits using it because "it's easier" but when you correctly earth the braiding it is not easier to install it's as easy to install armoured cable and you cut your fingers on the braiding and does not comply with the regs to boot. The braiding must be earthed or could potentially become live if the cable got bumped or damaged in some way. I would record as c3 if this is not the case, just a very odd cable for domestic use!
 
When we were taught terminating SY in college we were also always told the braid must be earthed but you must also have a dedicated CPC. The SY glands earth it anyway so don't see how it can be avoided unless plastic CU?
People always just use a 20mm plastic gland to enter the db and don't earth the braiding I installed a circuit in a factory and there were 4 sy circuits all like this on that db and probably hundreds across the factory
 
I really dislike sy cable for anything other than maybe industrial machine wiring, I come across it as a maintenance spark all the time and see mechanically biased engineers installing final circuits using it because "it's easier" but when you correctly earth the braiding it is not easier to install it's as easy to install armoured cable and you cut your fingers on the braiding and does not comply with the regs to boot. The braiding must be earthed or could potentially become live if the cable got bumped or damaged in some way. I would record as c3 if this is not the case, just a very odd cable for domestic use!
Where is it cited SY cable braid must be earthed and how do you confirm it can carry fault current without suffering undue thermal stress.
 
Where is it cited SY cable braid must be earthed and how do you confirm it can carry fault current without suffering undue thermal stress.
Well you have to tell us now Westward because we all want to know? :)
 
Lots of agree & disagreement on this,not the best cable to be used,on whatever.
The braid needs to be earthed,similar to the sheath of a Swa cable.
Doubt very much if the braid will carry the earth fault current,may do over a short time until the mcb,Rcd operates.
This I assume is why it’s not recommended nobody bothers to connect the braid,which really is a no no.
 
Lots of agree & disagreement on this,not the best cable to be used,on whatever.
The braid needs to be earthed,similar to the sheath of a Swa cable.
Doubt very much if the braid will carry the earth fault current,may do over a short time until the mcb,Rcd operates.
This I assume is why it’s not recommended nobody bothers to connect the braid,which really is a no no.
If a circuit is correctly designed fault current should only be for a brief duration nevertheless the braid must be able to withstand this. How are you deciding upon this when you connect it to earth.
 
Lots of agree & disagreement on this,not the best cable to be used,on whatever.
The braid needs to be earthed,similar to the sheath of a Swa cable.
Doubt very much if the braid will carry the earth fault current,may do over a short time until the mcb,Rcd operates.
This I assume is why it’s not recommended nobody bothers to connect the braid,which really is a no no.

It is designed as a machine control cable. Not for fixed wiring. I belive the confusion arose once manufacturers started producing it with Brown, Blue and GY core colours.

It also, only complies with the German VDE standards, hence not accepted by BS7671.

It's not UV or water resistant. The braiding is a screen, not designed to take fault current.
 
The braid is sometimes earthed for screening purposes only, so it doesn’t necessarily need earthing for the reason of fault protection only.
Perhaps should be installed with additional mechanical protection to reduce faults to a minimum.
Irrelevant in this scenario I know.

Only good for control wiring as stated by the manufacturers and should be installed as per manufacturers instructions.
 
Last edited:
If a circuit is correctly designed fault current should only be for a brief duration nevertheless the braid must be able to withstand this. How are you deciding upon this when you connect it to earth.
I’m not,it’s recommended the braid is connected to earth be it functional or protection,obviously the manufacturers,have tested this to their standards only.
 

Reply to Use of sy cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Interested in the groups interpretation of BS7671 with regards to the used of SY & YY cables. We have a commercial installation where we...
Replies
8
Views
2K
Hi Guys After bit of advice please as we don't do much data normally, tend to sub it out. Had garden building this week which we'd run in SWA...
Replies
9
Views
456
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
47
Views
8K
I have my AM2 coming up next week but something is puzzling me and I’m hoping someone can help me out. So there is some SY cable coming out of...
Replies
11
Views
2K
I have been carrying out an EICR on a property and have come across this black tarry substance on 2 of the cables. I have seen the pitch oozing...
Replies
9
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock