Discuss What is this black tarry stuff on the cable? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
I have been carrying out an EICR on a property and have come across this black tarry substance on 2 of the cables.

I have seen the pitch oozing out of a cut out before and I don't think it's this. Mainly because I thought that was only on the cut out fuse.

It's also not green, so it's not looking like the green goo.

It's extremely sticky and once it's on your skin, it's staying on until you've spent quite a bit of time scrubbing.

In the photo of the conductors coming out of the socket, you can see it all over the conductors. This circuit had a L/N - E IR reading of 0.36Mohms. There are damp problems in the property, especially at the socket in the picture. However, it is rising damp and the cable in next picture (explained below), is on the first floor on a non exterior wall, so I can't see the damp being anything to do with the black substance.

The other picture shows a 1mm cable sticking out of the wall with the black substance all over the outer grey insulation. This cable is dead and not in use.

Anybody know what the black stuff is?

tar1.1.jpg tar2.1.jpg
 
Last edited:
Hard to tell exactly but your options are either 1) it's a contaminent that's come from somewhere or 2) it's the plasticiser breaking down chemically. My money's on 2 but neither is great and will almost certainly be affecting the dielectric strength of the insulation.
 
If it's appearing from within the cable i.e. not something that could have oozed out of the building fabric, then I would agree that it is probably plasticiser escaping from the PVC, but of a type that does not attack the copper and therefore does not turn green. (The plasticiser that causes green goo is actually colourless, only turning green on reaction with copper.) The black might be mould, some PVC cables have a habit of turning mouldy even without visible leaching so it might be worse where it is actually breaking down, especially in a damp environment.
 
Melted adhesive from the insulation tape?
I did think of that. The one constant that I can identify is that they both had insulation tape wrapped around them. Still seems unlikely though.
 
I thought it looked like old insulation tape.
 
Well noticed. There does appear some odd black painty stuff. Perhaps an attempt to decrease damp seeping through.
I'll do the fault finding and hopefully dig up some more clues.
Looking at the exposed bits of wall in the picture with the cable sticking out could it be that the wall has been painted with blackjack or some other sticky black shmooo to waterproof it before being plastered? If so the messy sods have probably spread it over everything, cables included.
 

Reply to What is this black tarry stuff on the cable? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've come to a decision, I just cant do work anymore that involves mad stuff, for example today - 2 bed flat that's had fire damage, someone has...
Replies
4
Views
828
Hi, Any suggestions what this black cable is coming off the supply's incoming cable? Its a TN-S system, I thought it could be the earth conductor...
Replies
29
Views
3K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
837
Getting desperate to clear my small garage, and I have a bit of old red/black T&E. I used a few bits to add a socket or two in my flat and a...
Replies
5
Views
1K
Hello My dear old mother tried to clean the tiles in our utility room by using a damp rag and I think some water may have dripped into our plug...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock