Hi bud,i suppose there is no harm in listing abbreviated methods and sequences,but the most useful things to remember,are of a more general nature.
Like,to be fully conversant with the range of settings on any test equipment,and not to be immediately accepting,of results.

If it is tips to increase the speed of any tests,i am not the man to advise. Any testing and inspection,i have ever done,has taken as long as is necessary,with no exception.
 
I think beyond the obvious books, GN3 etc. there is no set way of approaching testing. Very broadly I would seek to establish the earthing arrangements first, while checking out the supply (cut-out, tails and so on) and effectiveness (continuity and ohms 0.05) and what was needed before delving in further as it is generally the most accessible area as well as one of the more fundamental requirements for all circuits. As no proper earthing = pointless doing any other tests.
I get a feel for existing circuits by doing the more accessible tests such as Zs on sockets, and anything else I can easily get to.
Although while I am doing this (eyes like a sewer rat) inspecting fittings, locations, damage, security (SADCOWS) and so on.
Having got a sense of there is nothing glaringly wrong I am then prepared to go in deeper with dead tests and so on.
Each installation is so different one can only roughly go through tests in the CRIPLER "system" if you like. It is usually the case that you approach each installation as what presents as the most urgent/dangerous or not as the case may be. To write a list etc. is re-inventing the wheel imo.
 
...Poor OP...he comes on for fire-fighting help...and you lot pass him a Peter Griffin novelty fire-extinguisher,filled with confetti ;)
 
Your all mad, Its the sheet floating about with all the the resistance readings of cables and protective device bs numbers and disconnection times etc

Did anyone produce new useful notes for form filling
 
I think the original form is still this one but obviously the Zs values are now incorrect following the introduction of Cmin.
However all the rest is still accurate.
You can also get various lists of Zs numbers that are current for taking into account Cmin.
and perhaps some BS numbers for reference.

You must surely know we are all mad by now!
 

Attachments

  • Useful Information for Electrical Form filling to BS7671.pdf
    412.3 KB · Views: 100
  • ZS chart_090315_final napit.pdf
    1.2 MB · Views: 83
  • British standard numbers reference list for electrical.pdf
    75.7 KB · Views: 86

Reply to Useful notes for testing electrical installations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Private tenant since 2011. First ever eicr February 23 informed via text it failed by text from electric secretary arranging appointment for...
Replies
12
Views
528
Hi I have an electrician over and he took over from an incompetent builder. The builder already installed the wiring but the electrician told me...
Replies
22
Views
865
I've just been to a job to replace a burned out switch where the customer supplied his own Arlec dimmer switch. During a dull moment, I read the...
Replies
6
Views
728
Folks it seems that we now have Issue 7 of the BPG#4 on EICR. Trying to compare them shows only minor changes, but those of note are: Page 9...
Replies
19
Views
1K
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
331

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock