teejay

Hello can anybody offer some advise. 3 phase lathe being moved in factory workshop . I have to extend 10mm singles in the trunking, upon investigation found the 10mm earthing conductor for the lathe has been taken from the metal trunking. I will probably rewire the earth back to the d.b. as trunking may in time become disconnected therefore losing earth continuity to the lathe, am I doing the right thing or can I rely on the trunking as being a reliable means of earthing.
 
if the trunking is electrically continuous, i.e. measure resistance ( low ohms ) from DB to point of utilisation. then it's OK to use . however, it's no detriment to add an additional cable cpc, and would possibly reduce your R1+R2,
 
Galv trunking is permitted for use as a protective conductor

543.2.2 (vi) refers.

You would need to ensure it's suitability for use though, joints etc.
 
Yeah just check your readings, I always put bonding links on trunking when I use it for earth, however I don't think theres any requirement to do so, so if they are not in place I would just check all screws on joiners etc.

Tis very common in industrial situation, and perfectly acceptable too, often giving very good readings.
 
Last edited:

Reply to using metal trunking as earth in the Australia area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
929
I have been asked to rewire an antique metal standard lamp. It has been rewired previously, but not earthed..! One of the screws on the base has a...
Replies
35
Views
5K
I'm working on a system that has been installed incorrectly. It's a 3ph Hager board with 8 swa cables glanded into the bottom entry panel. The...
Replies
28
Views
3K
Some friends are setting up a metal workshop inside a shipping container, on site at a commercial building that rents out studios, workshop space...
Replies
9
Views
2K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock