Discuss very high r1 result! in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
Afternoon all..

I have just been testing a ring final circuit and got r1 = 107Ω

It is TNCS, rN is 0.4Ω

I'm sorry I haven't got anymore results for you, I'm nowhere near home at the moment and those are the only 2 results I can remember.

This is on a kitchen ring and the Kitchen is being ripped out over the next week and I shall be reinstalling a ring in the new kitchen. This will be a good time to find any fault but...

My question is what could give this kind or result? 107 is huge! I initially thought loose connection, but even if the conductor was just brushing the socket terminal I would have thought it would be far lower than that?

Thanks..
 
Last edited:
how could appliances affect the r1?

Usually, for an intact ring, appliances connected wouldn't affect the result by enough to matter. However, if the line is broken, the measurement could well be via two (or more) appliances, if left plugged in and switched on. Part of the neutral conductor would be 'bypassing' the break in the line conductor, using the appliances to bridge line to neutral. Given the measurement of 107ohms for r1, this seems quite possible.

So the path could be: line (part) - load 1 - neutral (part) - load 2 - line (part)

Obviously, the measurement value would depend on the resistances of the loads in circuit.
 
My guess is the same as HandySparks, the L is broken somewhere, and you are measuring connected loads.
 
so how would the load resistance get from the load neutral back to the other L leg of the rfc? (always assuming that the N legs are dissed from the DB as they should be when measuring r1,rN, r2).
 
Usually, for an intact ring, appliances connected wouldn't affect the result by enough to matter. However, if the line is broken, the measurement could well be via two (or more) appliances, if left plugged in and switched on. Part of the neutral conductor would be 'bypassing' the break in the line conductor, using the appliances to bridge line to neutral. Given the measurement of 107ohms for r1, this seems quite possible.

So the path could be: line (part) - load 1 - neutral (part) - load 2 - line (part)

Obviously, the measurement value would depend on the resistances of the loads in circuit.

Yep,same test,loads disconnected,will answer that :icon12:
 
so how would the load resistance get from the load neutral back to the other L leg of the rfc? (always assuming that the N legs are dissed from the DB as they should be when measuring r1,rN, r2).

It would put the 2 appliances (at least) in series across L-L to bridge the open circuit. It would require at least one appliance plugged in and switched on at either side of the break / High res termination
 
Come across a few like that and the problem has been at the mcb, where one of the two cables has been put the wrong side of the little termination clamp.
cable ends would be out of the mcb for testing r1. nice try though.
 

Reply to very high r1 result! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Afternoon all. Bear with me on this one... Despite having been involved in the electrical industry for many years, I'm only just about to embark...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock