Afternoon all..
I have just been testing a ring final circuit and got r1 = 107Ω
It is TNCS, rN is 0.4Ω
I'm sorry I haven't got anymore results for you, I'm nowhere near home at the moment and those are the only 2 results I can remember.
This is on a kitchen ring and the Kitchen is being ripped out over the next week and I shall be reinstalling a ring in the new kitchen. This will be a good time to find any fault but...
My question is what could give this kind or result? 107 is huge! I initially thought loose connection, but even if the conductor was just brushing the socket terminal I would have thought it would be far lower than that?
Thanks..