Discuss Very odd problem what do you think ? in the UK Electrical Forum area at ElectriciansForums.net

Dave OCD

-
Mentor
Esteemed
Arms
Reaction score
6,671
I might be overlooking something that's right under my nose but opinions would be much appreciated. I visited a customer today with a detached garage supplied with power from a 13a RCD fused spur in the conservatory [spurred off RFC].
The RCD is 'tripping' randomly so I went to investigate.
The unit in question must be around 15 years old or more and immediately I found that the test button did nothing, a test at a garage socket also failed at x1 and x5 and the RCD refused to operate and I then found the same with the load disconnected testing at the spur itself. [SFCU in case of pedantry:)].
So after isolating and doing an insulation resistance test at 250v with everything switched on in the garage [freezer and lights] which showed around 40 Megohms L-E & N-E I fitted a brand new BG Nexus RCD SFCU, upon powering up the test button worked perfectly but in the garage both my tester and Kewtech plug in socket tester are showing L-E reversed ! :eek:
With the supply and load cables connected together everything is fine [Highest Zs is 0.79 at the furthest garage socket].
So I have another replacement unit to fit tomorrow, it has to be that, right ?
I can't think of anything else which could cause this but opinions are most welcome even if I'm being dumb. :)
Sorry about the long winded tale !
 
Hi - I was just going to suggest to check through the installation earthing. Perhaps a wander lead from met to that outlet so it's 100% that earth is where it's supposed to be :)

Thanks Wilko, yes I'm certain about that, with the new spur in place the garage lights wouldn't come on either. I'm 99% certain it's a dodgy unit but doubts creep in as it's brand new and I can't see how the internal circuitry could create this. But if I'm right it's a very dangerous RCD. :eek:
 
with the RCD out of circuit, then test for polarity. if it's right then then it is a duff RCD. dangerous and should be brought to manufacturers attention in case they have made a faulty batch.
 
with the RCD out of circuit, then test for polarity. if it's right then then it is a duff RCD. dangerous and should be brought to manufacturers attention in case they have made a faulty batch.

That's exactly what I did Tel, I know it has to be the RCD but it just seems so odd. I have another to fit in the morning so will update tomorrow, thanks.
 
Has the rcd unit also got surge protection as I have seen surge protection exstention leads showing crossed polarity when tested ,just a thought as I have notice some rcd sockets have surge protection fitted now
 
Yes SC but only after I'd removed the RCD and temporarily joined the supply and load together, with the RCD connected the MFT complained loudly. :D
 
No but that's a very good point, I'd convinced myself it had to be the RCD spur though as all was well with it removed and connected straight through from Conservatory to garage.
 
When a tester says line and earth reversed the comparative voltages are being measured and when you have a situation where this reversal is unlikely, as in your case, it is useful to note that the same comparative voltages would be measured if the outgoing neutral from the RCD were disconnected and there was a load connected at the end of circuit.
At the garage Line-earth would be 230V, Line-Neutral would be both the same at 230V (as the load would not drop voltage) and so the pd would be 0V, Neutral-Earth would read 230V because the Neutral is at 230V. These are the potential differences you would measure if Line and earth were reversed.

So in your case I would expect the original RCD had failed and that the neutral connection on the outgoing side of the new RCD is faulty to cause the symptoms you describe.
 
I'm wondering if it might be the RCD simply not putting the neutral through for example, then the internal tripping circuitry is fooling the MFT and socket tester into saying L-E reversal, I can't see how it could physically reverse L & E but convinced it's dodgy, I'll know for sure tomorrow. :)
 

Reply to Very odd problem what do you think ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
479
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
750
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock