Discuss Very strange Zone valve problem in the Central Heating Systems area at ElectriciansForums.net

Reaction score
236
Hi guys,

I have a really odd one for you all.

About four years ago we installed a heating systems for a swimming pool using various items but the main part of the heating was a Honeywell zone valve controlling the boiler.

The valve was controlled in the usual way via a programmer and stat, monitoring the pool water. Recently however we've been called back as the pool was loosing heat intermittently.

On inspection I found that the wiring was ok (no one had messed with it) but that some times, on heat demand, the valve wasn't turning enough to trigger the micro switch. So I bent the metal plate a bit so that it would press the micro switch earlier. This worked for a week or two but then the same thing happened.

I recommended changing the valve and this was done by a third party. This worked for a week but now the pool is loosing heat again.

I've not been back yet to see if it the same problem but if it is what could be causing the valve not to open enough?

I've not come across this is 25 years of doing working with these valves.
 
Certainly sounds like the valve is sticking. As above they may have just changed the actuator.
 
How does the thermostat determine the heat needed for the pool?
A sensor somewhere ,rather than the traditional way of a room stat reading the air temperature?
 
So has the probe been ruled out as the problem or possible settings/controls on the heat exchanger/boiler?
I know you mentioned changing the stat
 
I cant see it being the probe as if this was at fault it wouldn't cause the valve to 'half open'. it would just get the water temp wrong or not heat at all.

the only thing I considered was that the boiler was changed a while ago by a third party and although I've checked the wiring, which is ok, the new boiler is a Vaillant Ecotech and I noticed that when the valve does work, the boiler takes about 7 mins to fire up. I cant see that this is right. I know there are various installer settings on these boilers and I don't think the installer has done them correctly. That said, I don't see how this would affect the valve.
 
is it a genuine Honeywell replacement? I've had the cheap "corgi" branded ones where the head doesn't want to sit properly on the spindle, then if you tighten it right down onto the valve it makes movement stiff.
 
Just sharing some thoughts :)
Vaillant boilers have anti cycling feature and won't re-ignite if it's within the anti cycling period. This can be set from 2 min up. But if the boiler is cold or has been off for a period and the orange goes L there shouldn't be another delay. I agree with the previous replies and reckon the valve likely not fully opening, so microswitch not closing and no L on orange.
 
The original valve had a problem very similar to what you are describing and I had to loosen it off the base a little to get it to work. Honeywell told me that to refit the actuator the manual lever has to be pushed to the ‘manual open’ setting before refitting it. I couldn’t quite see why that was the case but that one had ‘Honeywell’ on the lid though.

The new one is a Honeywell unit.
 
Just sharing some thoughts :)
Vaillant boilers have anti cycling feature and won't re-ignite if it's within the anti cycling period. This can be set from 2 min up. But if the boiler is cold or has been off for a period and the orange goes L there shouldn't be another delay. I agree with the previous replies and reckon the valve likely not fully opening, so microswitch not closing and no L on orange.

I realise that no L on orange would cause the boiler not to fire. My question is why would the valve not turn enough to trigger the micro switch? It stops short. Brand new stat, complete valve, tested all outputs at each switch but the motor stops short.
 
Hi,have you measured voltage at the actuator when in operation?
Just a extra thought,as on rare occasions,damaged conductors or a poor connection,can hobble things,even with a paltry 20 odd watts added.

A high-five,for the 25W test lamp :)
 
So, been back today and the new valve was stuck in a position that wouldn’t trigger the micro switch. I moved the manual lever and suddenly the motor then moved the mechanism to the right position and the boiler fired.

When the stat was turned down the mechanism didn’t return as far as the old valve did.

Thoughts would be very welcome please.
 
This sounds like the operation of a 3 port valve. I think we are all assuming it's a 2 port valve. Can you confirm.

If it is 3 port then you need power to the white and grey to move the valve all the way and trigger the orange CFH to the boiler. If you only have power to white then the valve will only move to the centre position.

Could be that the wiring was altered when the new boiler was fitted and its been like this since then?
 

Reply to Very strange Zone valve problem in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

For the past few years, I have used a hydronic system (outdoor wood boiler) with both high and low temp working simultaneously. The low temp...
Replies
6
Views
776
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
981
1 - Major supply fault, details unknown. By time I get there DNO already put in genny and are digging up road. 2 - Reason for call, heating not...
Replies
4
Views
610
Hi all looking for some helpful advice I'm an Aussie so go easy on me, I have a good mechanical engineering head but first time plumbing and...
Replies
32
Views
2K
Having wired in parallel with my cordless programmable room stat an Alexa compatible wifi switch which has failed. I want to have a app...
Replies
1
Views
619

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock