Search for tools and product advice,

Discuss Volt drop in the real world in the UK Electrical Forum area at ElectriciansForums.net

TJC1

-
Reaction score
6
Has anyone ever had a volt drop issue?

Just for fun.......... yes i said fun, i cant believe i would be saying that in my mid 20s

But i did a calc for a radial circuit in in swa

B32 mcb
4.0mm 3core swa
35m run

(mV/A/m)

So...... 11X32X30/1000 = 10.56

Way over the 5% in table 4Ab

Am i missing something? Would the design current me lower as there is no way the circuit would pull 32a
 
Yes four marked faults caused by volt drop.

1) Algeria around 1982 in Algiers, we had a three phase 110 volt to neutral supply, and an air conditioning unit normally used in the 220 volt temporary camps, so 190 volt phase to phase, and the overload built into the compressor would regularly burn out as it stalled so often, even today most fridge/freezers say on the instructions not to use an extension lead as unless inverter control still same problem today.
2) A radio was transmitting mains hum as the voltage dropped to low for the power supply to smooth the output, this was in a caravan site.
3) A shrink wrap machine would not work correctly again because of volt drop.
4) A string of fluorescent lights and last 5 lights would not strike.

In the main the switch mode power supply has removed the volt drop problem, however we don't now when doing an installation what equipment will be used.

So...... 11X32X30/1000 = 10.56
Not quite if you correct the mV/A/m then 11.5935070873342 I put in the whole figure because it's so daft, when we can only measure the loop impedance to 2 decimal places, it is so easy to make mistakes with calculations I use a Java program, and I get the volt drop to 13 volts, but to measure we would measure loop impedance at incomer say 0.35 ohm then at end of run say 0.756 ohm now both can be out by 0.01 ohm so keeping rest of figures static, so 0.34 and 0.77 = shows 37 meters used and 0.36 and 0.74 shows 34 meters used. With 13.76 and 12.16 volt drop so in real terms we must allow for both errors on our measurement and the person passing the installation in the first place so it would need to be out by 4 volts before we could say an installation error has been made.

I have used installation method 100 never bothered changing it, but again if a 70 deg C or 90 deg C cable it will also change the results.

And a B32 MCB does not mean the design current Ib is 32 amp, it is normally considered with a ring final with a B32 that Ib is 26 amp.

It was my worry that if I did a PIR (now EICR) and I failed to spot excessive volt drop then some one could claim from me, however once one has done the calculations it becomes apparent you can't be 100% sure anyway, so unless wildly out, may be best to say nothing!
 
Run a 50M extension lead to the bottom of the garden and plug in a kettle full of water and see how long it takes to boil...vs plugging directly into the kitchen socket

This was one way I was actually physically shown as apprentice how volt drop affects a circuit
 
Just read this in "The Electricians Guide, 17th Edition" by John Whitfield, which may be of interest (page 79).

"If the actual current carried by the cable (the design current) is less than the rated value, the cable will not become as warm as the calculations used to produce the volt drop tables have assumed. The regulations include (in [appendix 4]) a very complicated formula to be applied to cables of cross sectional area 16mm^2 and less which may show that the actual volt drop is less than that obtained from the tables. This possibility is again seldom of interest to the electrician, and is not considered here."

Im not sure what this formula is (im not looking tonight) but it could be useful for peace of mind if for example a 10mm was just out of limits with the standard tables !
 
In my industry (railway) voltage drop is one of the largest problems we have to contend with.

Always remember that as a designer, the appendices (apart from 1) are informative, not normative. You are not obliged to follow the advice within. You'd be rather silly not to for every day work, but there are many circumstances where it's advantageous not to because it can often lead to significant inaccuracies. It's also worth remembering that the most important factor when determining suitable voltage drop isn't some arbitrary value in a book but the actual voltage tolerance of the equipment you're supplying. A closer look at the requirements set out in 525 will show you that the table in appendix 4 is ultimately there to aid calculation for worst case scenario.

One of the largest factors that affects voltage drop in my industry for example is cable operating temperatures. We spend a lot of time debating and correcting based on average weather predictions. Imagine for a moment a mile long length of black cable and how its resistance fluctuates based on whether it's been baking in the sun for a week or whether it's exposed to regular frosty mornings. Add to that the wildly fluctuating loads depending on time of year and the drop will fluctuate between the odd volt here and there to the odd hundred volts here and there.

We deal with this in a number of ways, chief among which is the use of step up transformers and automatically reconfigurable feeder switching arrangements. We also use equipment with very high voltage tolerance bands.

Essentially I can summarise my whole reply by saying that yes, voltage drop has real world consequences.
 
Essentially I can summarise my whole reply by saying that yes, voltage drop has real world consequences.

There is an upside to this. Within temporary power scenarios, particularly smaller, lower budget events (and some not so low budget marquee events) it can be a fight to convince a client that it is simply NOT acceptable to let them 'daisy chain' diy shed extension reels over unlimited distances to export DNO power from a building, instead of hiring a generator and distribution.

Voltage drop is the one aspect that will noticably impact straight away, whereas high Zs (and associated inability of CPDs to provide ADS within the required time) and the issue of exporting a TN supply outside of its equipotential zone are, to a layman, not considered or understood.
 
One of the dangers of a building site is the impedance of cables plugged into yellow bricks. With proper transformers there is no problem as the MCB's are fitted to the output, but the yellow brick often has a 10 or 12 amp overload on the incomer only, so at 55 volt to earth 10 x 230 = 2300 VA / 55 = 42 amp, and 1.5 mm yellow flex will not take 42 amp for long. With a single cable the resistance of the cable is low enough that is a scaffold pole falls and causes a line - earth fault more than 42 amp flows so the trip operates, but once you start plugging cables into cables you can't get the 42 amp needed to trip the overload.

I personally think the dangers of fire exceed the danger from electric shocks and a risk assessment would show better to use 230 volt now nearly every supply is RCD protected, so on a site not large enough for a proper 110 volt supply using 230 volt is safer.

I can't see how the yellow bricks comply, but it seems they are still used.
 

Reply to Volt drop in the real world in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
948
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
978
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
818
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock