hi, I have ariston boiler with volt free connection ,ta1, this should have been plumbed with 2x 2 port valves as recommended by manufacturer , but plumber has installed 3 port valve so we have to put relays in can anyone put me in right direction with wiring from wiring centre to relays?
 
Connect the orange of the valve and normally closed of the cylinder thermostat to one side of the coil, neutral to the other side of the coil, one side of the TA1 connection to common of the relay and the other side of TA1 Connection to normally open of the relay.

If you get an 8 pin relay base connect orange and normally closed of cylinder thermostat to pin 2, neutral to pin 7, one side of TA1 to pin 1 and the other side of TA1 to pin 3.

2 Pole 8 Pin 230VAC Relay Round Terminal - https://www.electrical2go.co.uk/2-pole-8-pin-230vac-relay-round-terminal.html

Round 8 Pin Relay Base - https://www.electrical2go.co.uk/round-8-pin-relay-base.html

Multi Purpose Enclosure - IP66 with 35mm DIN Rail - Solid Lid | QVS Direct - https://www.qvsdirect.com/multi-purpose-enclosure-ip66-with-35mm-din-rail-solid-lid-14665
 

Reply to volt free wiring on y plan in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
2K
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
974
Hello Guys, I was wondering if any of you nice chaps could lend me some advice. So I have an open vented heating system with a 3 port valve...
Replies
11
Views
2K
Hi there, the heating system I am working on has 6 zones and valves for each zone which was working fine with one boiler and one pump. some rads...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock