Discuss Voltage drop help please! in the Australia area at ElectriciansForums.net

T

ta-electrical

Hi, i am confused about how voltage drop is worked out and need an answer for the following please;

Work out cable size and cpc size you need when you have:
Cable length = 50 metres
Ib = 32Amps
to get a voltage drop that complies with regs i.e. below 5%(11.5 Volts).
It's wired in singles and enclosed in conduit trunking.

I tried to use the on-site guide and the tables it provides (page 166), i was using 'trial and error' on different cable sizes but, don't think i've been doing it right. Any help would be very appretiated and please if you get an answer refer to any sources you used such as the on-site guide.
I was using the formula that is in the on-site guide on page 124,
(mV/A/m)xIbxL / 1000.
On page 130, table 6D2 shows volt drops but, my answers don't seem to match what it says.
Thanks in advance.
 
transpose the equation. VD = ( mV/A/m )/1000 x Ib x L. put in the values VD=11.5, Ib=32, L=50. then

11.5 = (mV/A/m)/1000 x32 x50

mV/A/m = (11.5 x1000) / ( 32x50)

= 11500/ 1600

= 7.18

now look in osg for the casble size with a mV/A/M of 7.18 or less
 
Last edited:
So your saying to reverse the formula i.e. (mV/A/m)x32x50 /1000 = 11.5 into 11.5x1000 /50 /32 = (mV/A/m) ?

If i do that i get a value of 7.2, so would i have to choose a cable size with a resistance less than or equal to 7.2. e.g. 6mm by 6mm ?

Thanks for the help btw.
 
yep, you got it. it's just a case of juggling the equation you know 3 values so the unknown 4th value can be determined.
 

Reply to Voltage drop help please! in the Australia area at ElectriciansForums.net

Similar Threads

all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
734
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
894
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
878
Hi senior members of the forum, I need advice on couple of questions about Rio and BHP specs for electrical installation purposes. What is the...
Replies
0
Views
807

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock