Discuss Voltage Present on Earth Line in the DIY Electrical Advice area at ElectriciansForums.net

I thought we'd already established that i hadnt. Hence my question on what is the correct way forward in situations like this.

The established correct way forward for situations where the earth of a live installation is disconnected or missing is to connect it ASAP, ideally isolating the installation until it is connected.
For a situation where an out of the ordinary earth leakage is suspected then the way forward is probably to measure it first of all.
 
No not at all, the earth has a function in nearly all installations. It is normal and necessary to have a direct link between line, 230V and earth. This direct link can be a number of safety devices, like semiconductor type surge suppression, even some products that magically work without a neutral are using the earth, cables have a real capacitance between line and earth and as we have ac voltages, you will pick this up also. There is also other types of leakage due to magnetic effects, they all add up. I know its getting worse because more and more i am having to split an installation down into having multiple RCBOs rather than the standard 2 simply because of accumulated leakage current to earth, largely from electronic equipment. In simple terms and with very sensitive voltage instrument you will see 230V on a disconnected earth, always.

The actual current capability behind it is largely directly proportional to the size of the installation. I have seen earth currents of several amps and one thing is for sure, if i had disconnected it and touched the earth cable it would have really hurt.

Ok, this makes some sense. In my world the increasing use of cheap chinese SMPS's, especially in computer equipment, is definitely having an effect on inherent noise quality. That plus the use of crap zenor's (maybe the semi-conductors youre talking about?) as an after thought doesnt really address the initial problem in the first place. I could bemoan the loss of a good heavy linear PSU but then we all luv' a bargain dont we?

Im still surprised that there could be 240v on the earth line though. I guess everyday is a school day.
 
If you mean: 'Is it normal to have leakage current flowing into the CPC under normal conditions, that will give rise to a voltage if the CPC is broken' then yes, absolutely normal. All sorts of things cause a small amount of leakage - interference suppression components inside appliances, cable capacitance, normal atmostpheric moisture. The total in a normal installation might be a few milliamps, which is trivial so long as the cable is connected as it should be.

Exactly that. I neither expected or was aware that such a state could exist.
But, im still surprised at the extent that the earth line is used. Especially in my case where the machine is at standby. Had the motor been running i could sort of, maybe have justified it in my head.
 
Last edited:
The total in a normal installation might be a few milliamps, which is trivial so long as the cable is connected as it should be. Please put it back where it belongs. It is neither necessary, nor permissible, to disconnect it when a system is energised. Faults can be diagnosed without disconnecting it.

System was put back to normal as soon as i diagnosed the problem and in the interests of safety (and curiosity), ive now ordered a current meter. Im still uncomfortable using the washing machine and the meter was cheaper than replacing it. Although that might still happen if my OCD wins the day.

Again, ive learnt something and perhaps now appreciate the more puritanical postings earlier in this thread.
 
Last edited:
Im still surprised that there could be 240v on the earth line though.
I think that's your problem here, the misunderstanding of v=ir. Where for AC there r could actually be impedence.
If you have a 50kO resistor connected to line and the cpc, you will get a small current 5ma and nothing will go wrong
Disconnect the cpc and you will get 0v across the resistor due to no current flowing v=0mA*50kO therefore 240v to earth on either side, but very little shock. If you touch it a small current a few Mili Amps will flow and the voltage will be 150v or so and you'll feel a tingle.
 
I think whats missing here is application of basic dead tests

"seeing" 75 v on the CPC could simply mean the CPC is not continuous back to the fuseboard.
 
I think whats missing here is application of basic dead tests

"seeing" 75 v on the CPC could simply mean the CPC is not continuous back to the fuseboard.
I think he knew that (as he disconnected it). I think the problem was he doesn't understand why and whether it's a problem in itself.
Although you reminded me that you could test between all conductors and get 0v but you should really dead test to any bonded or earthed metalwork in the area as well.
 
Thankyou. An explanation that makes sense! Appreciate the time you took to write that down. Am i right in thinking this could also be described as an impedance issue with the DVM?
It's certainly not a Dvm "issue", A Dvm has input impedance as does an analogue vm. By asking that question it appears that you still have no appreciation of what you're actually measuring, and I suppose by inference.. (I'm too polite to finish that sentence).. It is however a "you performed a dangerous/stupid test" issue
 
I think that's your problem here, the misunderstanding of v=ir. Where for AC there r could actually be impedence.
If you have a 50kO resistor connected to line and the cpc, you will get a small current 5ma and nothing will go wrong
Disconnect the cpc and you will get 0v across the resistor due to no current flowing v=0mA*50kO therefore 240v to earth on either side, but very little shock. If you touch it a small current a few Mili Amps will flow and the voltage will be 150v or so and you'll feel a tingle.
That depends which end of the resistor you touch...
 
It's certainly not a Dvm "issue", A Dvm has input impedance as does an analogue vm. By asking that question it appears that you still have no appreciation of what you're actually measuring, and I suppose by inference.. (I'm too polite to finish that sentence).. It is however a "you performed a dangerous/stupid test" issue

No, please go ahead and finish.

But i suspect it would be more for your benefit than mine.
 
Ok, this makes some sense. In my world the increasing use of cheap chinese SMPS's, especially in computer equipment, is definitely having an effect on inherent noise quality. That plus the use of crap zenor's (maybe the semi-conductors youre talking about?) as an after thought doesnt really address the initial problem in the first place. I could bemoan the loss of a good heavy linear PSU but then we all luv' a bargain dont we?

Im still surprised that there could be 240v on the earth line though. I guess everyday is a school day.

I guess the best way to convince you is to rent an oscilloscope , make sure the probe screen is properly earthed and measure the voltage of the disconnected earth with the probe. As the oscilloscope has a very high impedance, some 1Mohn plus, i will eat my hat if you dont see 240V or whatever volts you have at the time. The use of any other instruments like an AVO or DVM simply hides the true potential as it is competing for the volts with the installation hence, depending on the type of instrument and setting you can get any volts you want. Hence my previous comments.
 
Im working my way through this in order to understand the situation a bit better. Link may help others who are as ignorant as i

The principles of Protective Multiple Earthing (PME) - https://www.voltimum.co.uk/articles/principles-protective-multiple-earthing

This is a different situation as its referring to differences in reference points wrt neutral and earth and also it highlights how dangerous PME can be if you do actually loose the neutral. It is not relevant to what i have been saying as i am talking about normal electrical leakage to earth by appliances that collectively in a large installation can present nasty currents through the body if you grab the disconnected earth wire whilst being pretty well earthed yourself either by holding onto steelwork or even standing in a puddle,,,lol
 
No, please go ahead and finish.

But i suspect it would be more for your benefit than mine.

It wasn't for my benefit and I don't do schadenfreude.
There are three issues here, all which have been covered by other posters to this thread, you didn't safely isolate, you disconnected the earth and you don't appear to understand the difference between voltage and current. The top and bottom of it is you did what you did because you didn't understand what you were doing. We all have to learn so I'm happy that you have.
If you want me to be perfectly honest, (for your benefit not mine) it was your (as I interpreted it) dismissive and arrogant reply in post #28, which swayed me to post, but you've learnt from that too...

I suspect your washing machine (and dryer) is (are) probably OK; if a spark comes to test the sockets ask him/her if they have an earth leakage tester and to check them out; (there are other ways to check but I don't want to be responsible for any mishaps).
 
It wasn't for my benefit and I don't do schadenfreude.
There are three issues here, all which have been covered by other posters to this thread, you didn't safely isolate, you disconnected the earth and you don't appear to understand the difference between voltage and current. The top and bottom of it is you did what you did because you didn't understand what you were doing. We all have to learn so I'm happy that you have.
If you want me to be perfectly honest, (for your benefit not mine) it was your (as I interpreted it) dismissive and arrogant reply in post #28, which swayed me to post, but you've learnt from that too...

I suspect your washing machine (and dryer) is (are) probably OK; if a spark comes to test the sockets ask him/her if they have an earth leakage tester and to check them out; (there are other ways to check but I don't want to be responsible for any mishaps).

Hilarious. I seem to have attracted the attention of the self elected forum guardian. A heavy mantle to bear, im sure! Whilst your first post is an attempt to insult my intelligence, the second is so drenched in sanctimony, im actually almost impressed!

Your misinterpretation of the word ‘issue’ also indicates a propensity towards our cousins over the pond. Perhaps you’ve been watching too many action movies - hence your caped crusader complex. Good luck with that one.

As with everything though, this thread seems to reached the end of its usefulness. Ive gleaned enough information to take away and digest (and yes, correct my understanding of basic theory). I freely admit i fall into the conscious incompetent league but hey ho, onwards and upwards.


Many thanks to Plugsandsparks, johnduffel and Lucien for their help and guidance without resorting to gazing over their noses. Fully appreciate it guys!!!

TTFN
RC

PS this one for w0z – ‘I’LL BE BACK!!!!’
 
Let's not get personal please, it only pulls the thread off course and often leads to more heated and baiting comments and the lengthy task of staff to read through all the thread and tidy where needed, please read the forums rules and expectations in the empty post box before you write your post, it is how we expect members to conduct themselves.
 
Last edited:
QUOTE - [ the fault is with the washing machine and dryer. Both are now unplugged until i can find a reasonable explanation for their behaviour. ]
I think you will find some leakage is allowed.
And appliances with heating elements seem to be the worst.
You should check with the mnufacturer how much leakage they allow for that product.
Just because there is some leakage doesn't always indicate a fault.
 

Reply to Voltage Present on Earth Line in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
650
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
561
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
782
I am sending power to some 5v led lights about 50ft from the transformer. I was going to use some CAT6 direct Burial cable that I kept after a...
Replies
2
Views
1K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock