Discuss Voltage problem. Help. in the UK Electrical Forum area at ElectriciansForums.net

S

Si Voodoo

Hi all,

Been to fit a new bathroom lamp. LED type.

Light is very dim.

Voltage between Live and Neutral is 103 Volts.

But between Live and Earth it's 203 Volts.

Any ideas what would cause this.

I'm going back to get into the loft tomorrow and see what's happening.

Previous electrician did a runner and would not come back and fix the bathroom light.

So why the reduced voltage between Live and Neutral??

Thank you.

Simon.
 
Basic testing of the lighting circuit cables would be advisable. Maybe the sparky has wired it so that your lamp is in series with another? Do some R1+R2 testing. And confirm L-N and L-E back at the CU. Were you testing with an MFT?
 
Thanks.

Didn't have time today, but will go back and do thourough tests and trace out this circuit.

I just used a Metrell voltage tester.

Will take the full kit tomorrow.
 
if it's the last light on the circuit and all the others work OK, then the fault will not be far away.
 
by arthur conan doyle... the case of the missing volts... available in paperback. £ 5.99.
 

Reply to Voltage problem. Help. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
626
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
561
Hi folks I've just identified as cause of lighting circuit tripping in consumer unit a low volts ceiling light with laride transformer taking in...
Replies
7
Views
228
Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
753
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
679

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock