Discuss Volts drop in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Hi.

You need the mV/A/m value for the particular cable from the tables in appendix 4 of BS 7671, the (Ib) (design current) of the circuit (not just the fuse/MCB rating), and the length of the circuit. Multiply these 3 figures together and divide the sum by 1000.

Maximum permitted volt drop is 3% (6.9V) for lighting circuits, and 5% (11.5V) for all other circuits.
 
Just a thought - If you use the formula that I gave, you need to correct your R1 + Rn value for temperature.

This is because volt drop calcs are based on conductor operating temps (eg 70 degrees) whereas your R1 or Rn measurement will be taken at around 20 degrees.

So, the actual formula would be:

Volt Drop = (R1 + Rn) x 1.2 x design current :)

This gives a pretty accurate answer.
 
Hi.

You need the mV/A/m value for the particular cable from the tables in appendix 4 of BS 7671, the (Ib) (design current) of the circuit (not just the fuse/MCB rating), and the length of the circuit. Multiply these 3 figures together and divide the sum by 1000.

Maximum permitted volt drop is 3% (6.9V) for lighting circuits, and 5% (11.5V) for all other circuits.

hi, why do we use the sum of 1000 to divide by?
thanks
 
hi, why do we use the sum of 1000 to divide by?
thanks

Hi mate,

It's because the figure used is mV/A/M (milli-volts per Amp per Metre) so you need to divide by 1000 to convert the milli-volts to volts, otherwise your volt-drop answer would be in mV instead of V.

Hope that helps:)
 
Last edited by a moderator:
If you have the book, BS 7671: Requirements for Electrical Installations (etc.....) Study Notes E1 (it's another big red book but with a spiral binding), it all starts on P8/1. There's loads of examples in there too.
 

Reply to Volts drop in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

I want to connect one panel 12 volts (south west) with 2 panel that are in series 24 volts (south) in parallel to a 24 volts in controller. The...
Replies
0
Views
479
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Replies
6
Views
2K
Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
626
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
733
Good evening all, I have been doing the C&G 2919-01 EV course via an online platform and have need to get the exam booked in...been quite busy...
Replies
1
Views
990

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock