Hi
I don’t know how resolve this so any helpful advice would be greatly appreciated. I have no electrical knowledge. I will try to be as clear and detailed as I can.
I’ve got a Bosch washing machine that’s two-and-a-half years old. Until early June, the machine has been flawless. But in June, my machine began intermittently tripping the electrics. At first it was one trip during the two hour cycle every couple of weeks, but this gradually grew to one trip almost every time I used it.
Naturally I presumed it was a fault with the machine because I don’t get any electrical trips when the machine is not in use. So I called Bosch and arranged an engineer visit. The engineer came and began by checking the mains power socket by plugging in a device with a bunch of LEDs on it. It didn’t show any faults. He then did some tests to rule out faults with the machine's major components (namely the motor and heating element).
He then unplugged the machine, pulled it out, took the back panel off and looked inside. After doing this, he said he couldn’t find any faults with the machine and suggested that the dedicated mains socket (for the machine) was faulty. Now this Bosch engineer had previously visited me two years ago when I had the same problem with my previous Bosch washer. Back then he also declared the machine fault free and said it was my mains socket at fault. He explained that the wires are likely worn out and this is causing the trip.
So I reminded him that he gave me the same excuse two years ago and asked him how my current washer was able to run for over two years without any problems. He said the wires inside the socket can get worn out, but sometimes it can keep working. I didn’t accept this explanation and asked him to remove the top panel of the machine to inspect the wires properly. He said he didn’t to do this and this started an argument. Anyway he ended up storming out.
I contacted Bosch and explained that I disagreed with the engineer’s conclusion and explained that I felt he didn’t inspect the machine properly. Bosch referred my case to their technical department and they came back and said that in their view the machine was inspected properly and is fault free. They said if the problem was with the machine the trips would be more frequent. Bosch said the likely cause of my problem is something called “nuisance tripping” as a result of earth leakage. They said I should contact an electrician and ensure that an RCD is fitted with a unit that has a symbol that I can best describe as two curly lines (my RCD doesn’t have this symbol).
Bosch told me I could get a second opinion from a second engineer, but that they stand by their technical department’s and the visiting engineer’s evaluation. I said I would be in touch when I had video evidence of the machine tripping.
From the day of the engineer’s visit (14 June), I filmed every last 30 minutes of the wash cycle as the tripping usually happens during this phase (where it goes through two rinse cycles, followed by a final spin) hoping to catch the fault on video and nothing happened. I filmed for two months and stopped a couple of weeks ago, having come to the conclusion that the fault had miraculously resolved itself.
Then today I run the machine and it trips the mains just as it was about start up its final spin. I reset the RCD and it completed the cycle from where it was interrupted. I just don’t know what to do now. I’m convinced the fault lies with the machine itself because my mains only trips when it is in operation. Nothing has changed in the last two months in terms of my electrical setup. A fault with the machine seems like the most obvious explanation. What I don’t get is why I had no problems since the engineer’s visit. If it really were the mains socket or my RCD, then how could I go 8 weeks using the machine without any trips?
I don’t know whether I should go back to Bosch or get an electrician to look at the RCD. Both will cost me (my machine is out of warranty). My questions are:
1. Where do you think the fault likely lies based on what I have described? Do you think it’s the machine or the RCD /electrics in my home?
2. Why do you think I have been able to get two months of fault free washing since the engineer’s visit? The engineer unplugged the machine during his visit. Could this have “disrupted” any earth leakage issues and given me some temporary relief from the intermittent tripping? (Usually the machine is permanently plugged into its dedicated mains socket.)
3. Do you think I should get in touch with an electrician or go back to Bosch and insist that there is a fault. I plan to start filming the machine again from tomorrow to get video evidence of it tripping during operation.
If you need any further information, feel free to ask.
I’d be grateful for any suggestions.