I recently did a load of work making good a poor installation for a friend who just bought a flat. I have some electrical qualifications and 30 years experience, but I'm not a member of a CPS because I don't do enough notifiable work for it to be worth paying the subs.

When it came to bonding, I only bothered bonding the gas and didn't bond the water pipes. I did this because the water incomer is plastic to 1 foot above the floor in the kitchen. There's literally 1 foot of 15mm copper pipe connected to the plastic incomer in a cupboard under the kitchen sink with a stop tap in it and after that, it's all plastic joints and more plastic again off to the boiler and shower.

Once I'd finished, I got a CPS registered electrician out to do a condition report on the place for me so that my work had been verified by someone else. I explained my reasoning for not bonding the water and asked if he was happy with that.

He told me that I had to bond the water, even if it's plastic because the "water can become live".

Is this a thing? I can't find anything about live water in my regs book on the subject of bonding water pipes. I thought the point of bonding metal pipes is that if they were stuck in the ground somewhere, they might introduce a dangerous earth potential into the installation? I don't really see how that can happen with plastic pipes.

I've added the bonding as he requested since I don't see it can do any harm. Was I missing something?
 
Recently had this issue with the Niceic man.
Being old school you would of bonded it,but these days if the entry into the premises is plastic then no need to bond .
Even when copper pipework comes away from the plastic pipework.
 
That’s two in two days we’ve had on this subject.

As above, no need to bond, it’s a waste of cable.
 
Theoretically if the water is conductive enough, it could bridge the gap between the metal pipe in the ground and some other unbonded section of metal pipe accessible to the touch, with a low enough resistance to introduce the ground potential into the equipotential zone. However, in that case, the water is probably badly contaminated and a miniscule risk of electric shock is overshadowed by whatever poisoning you are likely to get from it.

In water-cooled high power electronics where the hot-side heat exchangers are at high potentials and isolated by plastic piping, it is necessary to de-ionise the water and monitor its purity to ensure it remains a good enough insulator not to cause earth leakage and electrolysis in the cooling system.
 

Reply to Water becoming "live" in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
925
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
428
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Wonder if anyone can help out, my experience in heating is minimal. So house I was working in had a circuit for the water heater, which went to a...
Replies
4
Views
352

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock