Bit of an odd one this and I just wanted to run it past bigger brains than mine to make sure I'm not missing something obvious.

A brand new PME supply is being brought across to a field which has got 3 outbuildings, all of which need lights and a couple of sockets.

The supply comes to the first building, and is going to run in armoured out to the next and then onto the 3rd building. Each building will have it's own mini 'garage' C/Unit with RCD etc. In the third building there is a solitary sink which is the only water supply for the whole place and the only metal incoming service pipe.

My initial thought was to bond from the MET at the 3rd C/U in the building with the sink, but I've suddenly just had a panic that I ought to be taking the 10mm cable all the way back to the original MET at the 1st board where the supply comes in.

Then I started doubting myself even more - the incoming supply to the 3rd building is 6mm 3-core armoured on a 32A breaker - it seems mental to have a water bond in 10mm when the main earthing conductor for that building is only 6mm?


So, my question is:
10mm water bond back to main MET on 1st board?
10mm water bond to MET on 3rd board?
6mm water bond to MET on 3rd board?
any other options!?!?

Hope that makes sense - it's been a long day and my head hurts - the beer hasn't kicked in yet either ;-)

Thanks for your thoughts!
 
Main bonding of services should go back to the MET at origin.
You are trying to ensure that the services have the same potential as the MET in fault conditions with no significant voltage drop.
The Main bonding (for PME) is sized according to the supply neutral conductor size and can be larger than the earthing for any individual sub main.


For your situation, assuming your supply neutral does not exceed 35mm², I would tend to supply the buildings with 4 core 6mm² and double up two cores to provide an earthing and bonding conductor throughout. Then you can link the EMT at each building back to the MET without problem.


I can't quite make out if the cables have been laid already or if this is in the planning stage.
 
Main bonding of services should go back to the MET at origin.
You are trying to ensure that the services have the same potential as the MET in fault conditions with no significant voltage drop.
The Main bonding (for PME) is sized according to the supply neutral conductor size and can be larger than the earthing for any individual sub main.


For your situation, assuming your supply neutral does not exceed 35mm², I would tend to supply the buildings with 4 core 6mm² and double up two cores to provide an earthing and bonding conductor throughout. Then you can link the EMT at each building back to the MET without problem.


I can't quite make out if the cables have been laid already or if this is in the planning stage.


sort of mid-way through! I thought I had it all sorted and then discovered this water pipe in the final building.
it's too late to change the main armoured cable, so I'll just have to run an extra 10mm single back to the MET.
Poo bum. I'll remember your idea for next time though!
 
as long as it has 30mA RCD for all circuits, divorce the 3rd building from the earthing system and make it TT, cheapest option.
 
Don't have to run another conductor, can make the outbuilding with the sink TT.
Depends what's cheaper?

Good idea. Definitely cheaper/quicker.
so what do I do with the 'spare' Earth on the incoming SWA? It has to remain connected at building 2 as it's the cpc for the sub main, so I just snip short of the connection at building 3 and tape it up?
 
Good idea. Definitely cheaper/quicker.
so what do I do with the 'spare' Earth on the incoming SWA? It has to remain connected at building 2 as it's the cpc for the sub main, so I just snip short of the connection at building 3 and tape it up?

no. you gland it into a plastic ad. box or mnini CU, but don't banjo it or take the cpc anywhere into the installation of the 3rd building.
 
Evening all.

Bit of an odd one this and I just wanted to run it past bigger brains than mine to make sure I'm not missing something obvious.

A brand new PME supply is being brought across to a field which has got 3 outbuildings, all of which need lights and a couple of sockets.

The supply comes to the first building, and is going to run in armoured out to the next and then onto the 3rd building. Each building will have it's own mini 'garage' C/Unit with RCD etc. In the third building there is a solitary sink which is the only water supply for the whole place and the only metal incoming service pipe.

My initial thought was to bond from the MET at the 3rd C/U in the building with the sink, but I've suddenly just had a panic that I ought to be taking the 10mm cable all the way back to the original MET at the 1st board where the supply comes in.

Then I started doubting myself even more - the incoming supply to the 3rd building is 6mm 3-core armoured on a 32A breaker - it seems mental to have a water bond in 10mm when the main earthing conductor for that building is only 6mm?


So, my question is:
10mm water bond back to main MET on 1st board?
10mm water bond to MET on 3rd board?
6mm water bond to MET on 3rd board?
any other options!?!?

Hope that makes sense - it's been a long day and my head hurts - the beer hasn't kicked in yet either ;-)

Thanks for your thoughts!

The reason the main bond has a larger cross sectional area requirement for PME/TNCS installations is because you are effectively creating a parallel path for return currents by connecting the neutral to a conducting service at earth potential. Therefore a significant current can flow through the bond when then installation is loaded.
 

Reply to Water Bond size on outbuilding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
347
Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Replies
5
Views
973
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock