With rcbo off but main switch on 8 - 10 ohm between l and e on continuity tester. Ir test is greater than 299 on every circuit
[automerge]1570137908[/automerge]
With main switch off, the 8-10 ohm disappears but the tester just clicks on off on off on off for continuity
 
Turn the main switch off you are getting continuity because neutral and earth are connected external to the installation.
 
With rcbo off but main switch on 8 - 10 ohm between l and e on continuity tester. Ir test is greater than 299 on every circuit
[automerge]1570137908[/automerge]
With main switch off, the 8-10 ohm disappears but the tester just clicks on off on off on off for continuity
Sounds like your picking up the circuitry within the RCBO. What continuity do you get with the RCBO disconnected?
 
What disappears. Randomly changing components is only guesswork you need to find the actual problem causing the issue.
 
I never randomly changed anything. As i said the 8 ohm disappears when the live and neutral disconnected from rcbo so i suspected a faulty rcbo. I changed it to see if a new one had tbe same result. It did.
 

Reply to Weird Earth Fault in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening all. Been at a property the last couple of days that had suffered damage due to a surge. I got the power back on all circuits apart from...
Replies
17
Views
2K
Hi, I've got a light with a ceiling rose in the kitchen. While rectifying some faults in the house I came across to the light and measure Neutral...
Replies
25
Views
5K
About 5 years ago during a full refurb on my house I re-wired the property myself (old aluminium wiring) in line with 17th edition. I had it all...
Replies
4
Views
1K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the...
Replies
25
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock