Hi guys,

I'm doing some revision for 2391 and I've built a test rig to practice on, just one radial (lights) and a ring.
The testing was all going fine until the IR tests.

Results were as follows

Whole installation:

R1 to Rn = 0.13MOhms:eek:
(R1+Rn) to R2 = >299MOhms
R1 to R2 = >299Mohms
R2 to Rn = >299Mohms

:confused:

I thought I must have made a stupid mistake when wiring up but individual IR tests on the radial and the ring all come out as >299MOhms.

long story short, I put the probes across the RCD inl the various Phase to Neutral combinations and found that when the rcd was off putting the probes at the bottom gave a reading of 0.24MOhms

as shown here:
notoksmall.jpg


When it was switched on the reading stayed the same then when I switched both the RCDs on with neither the ring or radial connected the reading dropped to 0.13Mohms indicating a parallel path through both rcds?

Boths RCDs behave in the same way

The 100A breaker checks out ok.
Are these just a pair of crap/dangerous RCDs or am I being a berk?
I realize that I've probably made some stupid mistake or am ignoring some blindingly obvious reason for this but I can't see it!

Any comments or suggestions gratefully received.

cheers
Ben

PS I should just say that before I posted this I removed all wiring except that which came with the board and retested with the same results.
 
Last edited by a moderator:
Sounds like you're reading through the RCD internals. Disconnect line and neutral from the relevant protective devices before carrying out IR tests.
 
when your doing the test remember IR method 2 in GN3 isolate combine phase and neutran and then test between them and earth means you have no potential difference between line conductors so no need to strip out lights ect. far faster as well.
 
when your doing the test remember IR method 2 in GN3 isolate combine phase and neutran and then test between them and earth means you have no potential difference between line conductors so no need to strip out lights ect. far faster as well.

that actually makes a ton of sense. I did in fact perform that test and got >299 on the whole installation but couldn't work out why I was getting dodgy readings from r1 to rn.

That little nugget allows another piece of the puzzle to slot into place.

Thanks!

Ben:D
 

Reply to weird IR test results with RCDs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
872
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hello everyone, I saw in the hospital every circuit has 2 separate cpc, same size, sometimes different. I'm wondering. How we can do the dead...
Replies
1
Views
924
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock