Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the insulation resistance stage.

testing between Neutral and earth I got a dead short. so split the circuit and narrowed it down to a 1ft long length of cable bewteen the DB and a generation meter. everything else was clearing no issue but this seciton was still dead short.

now heres the thing when testing just the cable i.e taken out of the bus bars. the cable cleared but when they where connected in it was a dead short.

at the time this was on the RCD side of the a split load board. the solar was using and MCB and the RCD had been changed for an A type the neutral was installed on the RCD neutral bar and the earth was installed in the rest of the earth bus bar.

any ideas what might have made this happen?

in the the end I installed the solar circuit onto it own RCBO and the fault was cleared but would like to know any suggestion as to why i might have been
 
Welcome to the forum.
Especially as you are only up the road from me - I'm in Oswestry.
at the time this was on the RCD side of the a split load board. the solar was using and MCB
Best not to do that. If the RCD trips, the solar can still feed every other circuit on the RCD side until the inverter notices the lack of incoming mains, which I've known take 500ms.
So I'm glad you went for the RCBO approach in the end.
testing between Neutral and earth I got a dead short. so split the circuit and narrowed it down to a 1ft long length of cable bewteen the DB and a generation meter. everything else was clearing no issue but this seciton was still dead short.
Forgive me asking the obvious question - what was the earthing arrangement? TNCS?
And was your RCBO single pole or switched neutral?
 
It was on a TNS earthing arrangment and the RCBO was double pole.

Thats good to know about the inverter potentially back feeding into other circuits wasn't aware that could happen. I normally put everything on RCBO or install its own RCBO consumer unit. but in this case the guy was replacing his board and his only spare ways were on the RCD side.
 
It was on a TNS earthing arrangment and the RCBO was double pole.
Sorry - it was too obvious not to ask!
So you basically had 0 Mohms between CPC bar and the N bar for that side.
But the N and CPC for the PV circuit was clear.

Some random possibilities...
1 - N-E fault on another circuit, normally 0.00 Mohm would mean instant RCD trip unless it wasn't working?! Did you happen to try a continuity test too?
2 - bonding to services effectively created a link to another property which is TNCS; RCD and main switch would both have to be on/closed for this to work.
3 - for whatever reason a mistake was made identifying the earthing type. Do you remember if PSCC and PEFC were the same?
 
N-E fault on another circuit, normally 0.00 Mohm would mean instant RCD trip unless it wasn't working?!
Not by any means a certainty. A reading of 0.00 MΩ displayed on an insulation test could be as high as a few kilohms, or over over 10kΩ if you allow the +/- one count. E.g. 5kΩ= 0.005MΩ. With the few volts likely to exist between neutral and earth, the resulting leakage current is likely to be less than a milliamp.
 
Do you mean you're not supposed to RCD protect solar if the RCD protects other circuits?

Definately not, this is potentially lethal!

A solar system is a source of supply, it effectively generates power.

If a person comes into contact with a live part and receives an electric shock then an RCD will disconnect the supply before that shock becomes fatal.
But if the outgoing side of the RCD has a second source of supply connected to it, such as a solar system, then the RCD will only disconnect the DNO supply whilst the solar continues to generate power and kill the person who would otherwise have survived.
 
The RCD must not be shared with other circuits. If RCD protection is required then it still must be fitted.

Surely it would need to be fitted at both ends of the circuit if RCD protection is required otherwise the solar will still maintain that circuit in a live state if the RCD trips.
 

Reply to Weird?! Neutral-earth fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
412
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
357
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock