6mm 4 core flex has a vd of 6.7mV/A/m. So 15m of it has a neutral conductor vd of 0.1V/A or 1 Volt for every 10A. For 20A through each RCBO and SP supply vd neutral is 3 x 20/10 x 1 = 6V
It has a CCA of 32ishAmps. Might the neutral be undersized when operating from a single phase supply? 3 x 20A = 60A?
http://www.aeicables.co.uk/literature/CurrentRatings.pdf
Do you have a DVM with capture mode to examine the N-E voltage at power up. Some RCBOs use a rise in N-E voltage to detect loss of neutral and initiate a trip. That is why they have a functional earth.
It has a CCA of 32ishAmps. Might the neutral be undersized when operating from a single phase supply? 3 x 20A = 60A?
http://www.aeicables.co.uk/literature/CurrentRatings.pdf
Do you have a DVM with capture mode to examine the N-E voltage at power up. Some RCBOs use a rise in N-E voltage to detect loss of neutral and initiate a trip. That is why they have a functional earth.