Discuss Welder taking out MCB in the Electricians' Talk | All Countries area at ElectriciansForums.net

A

ash_s3

Hi
I recently installed a supply for my mates welder in his workshop.
2.5mm SWA from existing TP Schneider DB to 16A wall mounted socket.
Protected by 16A Type C MCB.

Welder has a 16A blue plug attached and this is how it came from the manufacturer.
The breaker trips after one or two welds, i then upped it to a 20A C, same thing, then i went up to a 20A type D and still cant use the welder anywhere near full power.

Cable meggered out all clear (only a 10m run), nice low Zs, all connections double checked etc..

Surely if the welder comes with 16A plug attached it cant demand anymore current that 16A as that would overload the socket.

Im thinking faulty welder, any one any thoughts?

Welder is an SIP IDEAL 240.

Thanks
 
Last edited by a moderator:
Did you test the current draw with a clamp on ammeter? Maybe the welderis tracking internally across the windings. This wouldn't show up on an IR test.
 
Not had chance to test with clamp meter, its on another van.
Haven't IR tested the welder, only my wiring.

How can it require a 40A fuse and come fitted with a 16A plug? Where did you find this info please Lenny?

Thanks guys
 
Lost count of the number of times I have seen a single phase mig welder on a 13 amp plug top, take out a 32amp ring main mcb. Open the plug top and there a nice peice of wire rapped around the fuse carriers prongs. These babies draw a lot of current. As Lenny says that model needs a 40A supply, and trust me, if handled badly they can take the DNO's HRC out no problem. Take care.
 
So i need 10mm SWA on 40A MCB with a 16A socket? Thats never right surely?
The thing has only got a 2.5mm flex on it!
 
Yes, well, kind of, you get a63Amp plug and socket. Check out the Gewiss range on one of your local websites.

That supply cable at 2.5 mmsq isn't going to cut the mustard at 50Amps either.
 
Remember, these things are not your domestic friendly resistive loads. That highly inductive arc is caused by something close to a short circuit. Make sure the suppliers cut out fuse can handle it. As I have said on domestic supplies the standard HRC's used can easily be taken out.
You are upping your supply cables and your MCB's.
In doing so you are reducing descrimination between primary and secondary over current devices. Be carefull !!

Oh and in case you ask. Surge arrestor at the mains position. (I have found them capable of sorting the problem in the past)
 
Last edited by a moderator:
no chance this would be a 2phase model (aka 3-phase)

would have been better. on the tpn board anyhow

should be 1phase with the 16amp plug-but plug and lead don't seem to match SP specs
 
Last edited by a moderator:
The supply cable will obviously need to be upped to 6/10mm (havent looked it up yet)

What about the flex on the welder?

Personally I’d return it as “not fit for purpose” and get a model that suits the supply. 40A is one hell of a whack for a home welding kit.

I can just imagine, Sunday morning he goes to do a bit of DIY while his wife puts the dinner in the oven. One DNO cutout launched in to space!
 
For some reason this PC has found a new trick. Have now got the fonts sorted, it’s started doing double posts!
 
Last edited by a moderator:
Thanks Tony, this welder is being used in an industrial unit for a metal fabrication business so needs to be fairly hefty for welding 10mm plate.SIP have emailed me confirming it needs a 40a supply and the chap was unsure why it had a 16a plug attached! He Said the 2.5mm flex was ok as it only draws 40a for a small amount of time then settles to around 30a!!
 
you would stand a better chance with the 20amp 3-phase model if it could be swapped at all


you may even get away with the existing 2.5 final circuit assuming it utilises only 2-phases

which i think is the case


why is a 40amp SP welder supplied with a 16amp plug and 2.5 lead? nothing surprises me with new equipment lately
 
Last edited by a moderator:
so it's an old model -wonder if it came pre-wired at all?


looks like the lead+plug and final circuit are undersized then

also you'd need to check the suitability of supply and sub-main for SP welder


i would prob try welder at sub-board

as you might still be underpowered even with new final circuit


it'll be simpler if all existing loads are SP rather than 3P
 
Last edited by a moderator:
Along time ago I tried using my SP SIP 105 mig to weld a friends narrowboat. On the canal bank, on an extension lead about 50 M from the plug (on the canal side).

As you can imagine, it was like as much use as platting fog
 
Dave, there is no sub board. Its a small unit on an industrial estate, 3Phase supply - TNCS going straight into 3 phase Schneider DB.

SiP said the welder uses 30A constantly on max power, but can draw a peak 40A for a very small amount of time on initial start-up, would a type C/D curve 32A MCB allow for this, that way i can use a 4/6mm SWA and use 32A socket and plug without exceeding the rating of them.

What a pain in the arse this job has turned into! Started with... "can you just wire a 16A socket in for me"
 
ok sorry i though it was a shed or something

i'd prob test it at board on D type mcb, see if it's working properly and then size final circuit if all goes well

volt drop shouldn't be an issue on IND unit if there's spare capacity on a phase
 
Last edited by a moderator:
Along time ago I tried using my SP SIP 105 mig to weld a friends narrowboat. On the canal bank, on an extension lead about 50 M from the plug (on the canal side).

As you can imagine, it was like as much use as platting fog

i'm hoping to learn how to weld soon:yesnod:-never got round to it
 
It's bl00dy brilliant fun.

Although the welds can hurt as you look at the drip metal on your arm, and then 3 seconds later realise its working its way through your arm like chernobyl is working its way through the earth on its way to china
 
ok sorry i though it was a shed or something

i'd prob test it at board on D type mcb, see if it's working properly and then size final circuit if all goes well

volt drop shouldn't be an issue on IND unit if there's spare capacity on a phase

How do you mean 'test it at the board on a D type MCB'? Wire the welder flex into the DB on the 32A MCB and check it doesnt trip?
Can you get 4mm flex?

The board is literally empty, 1x Ring main, 1x Water heater, 1x Lighting circuit
 
Last edited by a moderator:
I’m about to buy a Stahlwerk CTM-250ST.
I contacted them about a note on website regarding residential use and electromagnetic interference. Their clarification was with regard to public low power supplies and danger for people with pacemakers. I also asked about electrical supply suggesting 32A/40A Type C MCB ON 220/240 circuit. Their response was: “ I need a 16A socket outlet and 16A Type C
 

Reply to Welder taking out MCB in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

Got an EICR testing to do on a site soon. Some was done 2018, some 2014... but their office cant find the reports... So got to start from scratch...
Replies
63
Views
7K
Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
Replies
18
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I realise this overlaps with the Earth Rod install post a little, but I am attempting to plan part one of an upgrade. Currently I am mostly...
Replies
24
Views
6K
Hi I am a sparks from the 15th Ed, did 16, 17 and last year 18th. I am out of practice though as have been office based for 12+ years in a...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock