Discuss Wet Riser Pump back up supplies in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Refurb on an existing building where new wet risers are going in:

Where do changeover switches for back up supplies for wet riser pumps have to be installed? Can they be installed at the main switchboar with a single cable to each pump or does the changeover switch have to ne local to the pump with 2 supply cables? Where are there regs on this?

Also I have been told by fire specialist that the supply has to be able to take the locked rotor current of all fire pumps............I have been told that 2 x 75kw pumps are going in with a LRC of 900 amps each! This seems like an unfeasable requirement ( the existing substation which supplies the building is only 1000KVA). Does this also apply to the back-up generator? Has anyone had this thrown at them before?

Any insights are welcome. Thanks
 
What do the drawings and specifications say, surely a job like this can't be done by word of mouth, there must be some paperwork somewhere.
 
http://www.bafsa.org.uk/wp-content/uploads/bsk-pdf-manager/2017/06/BIF-21-Wet-Dry-Risers.pdf

Please see page 3 of 4 of the BAFSA document on wet riser pumps and their power supplies. It does not answer your question completely but there are some contact numbers at the end of it. If they don't know they might be able to direct you to someone who does.

Also IFEDA - the Independent Fire Engineering and Distributors Association.

See: ifeda.org

I'd have thought BS9990 has something to say on the matter.

Lastly: High rise wet riser fire systems installation | UK Dry Risers - http://www.ukdryrisers.co.uk/wet-riser-systems.php
 
Last edited:
What do the drawings and specifications say, surely a job like this can't be done by word of mouth, there must be some paperwork somewhere.
There is a spec and drawings (layout only) but the spec says things like “supply to specialists requirements”, and the specialist isn’t committing to much.
 
http://www.bafsa.org.uk/wp-content/uploads/bsk-pdf-manager/2017/06/BIF-21-Wet-Dry-Risers.pdf

Please see page 3 of 4 of the BAFSA document on wet riser pumps and their power supplies. It does not answer your question completely but there are some contact numbers at the end of it. If they don't know they might be able to direct you to someone who does.

Also IFEDA - the Independent Fire Engineering and Distributors Association.

See: ifeda.org

I'd have thought BS9990 has something to say on the matter.

Lastly: High rise wet riser fire systems installation | UK Dry Risers - http://www.ukdryrisers.co.uk/wet-riser-systems.php

Thanks for this BS9990 has basically answered my first question. I will call around to clarify.

Thinking about the LRC problem it may not be so onerous if it is for a very short period of time that this is required....,ie more than the amount of time it takes for the pump to burn out. I will do some more digging.

I appreciate the help.
 
There is a spec and drawings (layout only) but the spec says things like “supply to specialists requirements”, and the specialist isn’t committing to much.
Probably doesn't know whats what anyway
 
I think you may need to clarify how the pumps are to be operated ie:

1. Both running at the same time in which case you probably need a scheme for sequential starting one then the other.

2. Master and standby - one nominated to start first and the other only starts subject to some conditions such as perhaps low pressure or Master fails to start in which case standby auto-starts or has to be manually started .

You get the idea.
 
I think you may need to clarify how the pumps are to be operated ie:

1. Both running at the same time in which case you probably need a scheme for sequential starting one then the other.

2. Master and standby - one nominated to start first and the other only starts subject to some conditions such as perhaps low pressure or Master fails to start in which case standby auto-starts or has to be manually started .

You get the idea.

Your right I will seek clarification.
I am pretty sure it is master standby. My concern is that they are asking for supply sized for both pump in LRC condition. I guess the main pump could lock and the standby could kick in then lock as well. Then the problem could clear and the supply would have failed before the pumps. As previously noted I will see if I can find out how long it takes for the pumps to burn out as long as the supply does not break in a shorter time than this I can’t see the point in sizing to LRC for a longer period. Thanks again for help.
 
Would you mind writing another post once you have squared away your questions? It adds to the wealth of knowledge of all of us and our interest - otherwise we are left hanging.
 
You are dealing with something which could be deemed a safety system. Get an experienced person to design it for you or pass it over. By safety system I mean peoples lives could rely on what you are installing.
 
You are dealing with something which could be deemed a safety system. Get an experienced person to design it for you or pass it over. By safety system I mean peoples lives could rely on what you are installing.

Whilst I agree with this statement finding someone who does have experience and is willing to commit to anything is proving tricky..... do you know anyone?
 
Update: I have found an excellent guide to this:

BSRIA BG 70/2017 Life Safety and Firefighting Power Supplies

I have not fully read it but it looks like it is going to give me guidance on all my questions.
 
Would you mind writing another post once you have squared away your questions? It adds to the wealth of knowledge of all of us and our interest - otherwise we are left hanging.


Marconi,

Here is what I have found out:

The ATS needs to go by the pump control panels (this is pretty clear in BS9990). This makes sense in terms of better redundancy (2 sets of cables over diverse route). The mains monitoring for generator control should be at the ATS.

As you noted to design the supply you need input on worst case scenarios from the specialist (something I am pursuing). However in very general terms: The mains supply and the back supply need to be designed in accordance with: All the normal stuff you would associate with a motor (starting current, motor rating, efficiency, pf, , starting volt drop, FLC etc.), and the supply and cable must be able to take 150% of the FLC , and it must hold under LRC conditions for 1 pump for 75% of the time it takes for motor burn out. This Basically means appropriately sized BS88 fuses feeding FP600S cables on separate diverse routes feeding the ATS. The fuses need to discriminate with the specialists overloads in the pump starter (I am assuming the specialists overloads need to adhere to all the above as well so I am expecting my fuse and cable sizes to get quite big). Thanks for pointing me in the direction of BS9990. The document which really sorted it for me was BSRIA BG 70/2017 Life Safety and Firefighting Power Supplies.
 
There may even not be any overloads in place within the starter.

That would make sense for a pump that you want to run to destruction. I have asked the question of the specialist, along with details of motor burn out time etc. He is going to ask his supplier. I will let you know the outcome if interested.
 
Thank you for taking the time to report back. When I ran the engineering for a strategic site I used parsons brickerhoff to calculate and select high current fuses and circuit breakers and ensure discrimination and trip settings for large motors. They had an electrical modelling tool which could take a design - cbs by make and setting, fuses by make and rating, cables by make and length, load by type and use profile, even ATSs, etcetera and do runs on it to show that an electrical design would perform as required. I used the London office but I note they have an office in Bristol too. Sorry I don't have a contact - it was 15 years ago. So if you design the installation they could do modelling on it and confirm all is well, or they can help you design, source components and test it.

Electrical engineering - http://www.wsp-pb.com/en/WSP-UK/What-We-Do/Services/All-Services-A-Z/Electrical-engineering/
 
Last edited:
http://www.bafsa.org.uk/wp-content/uploads/bsk-pdf-manager/2017/06/BIF-21-Wet-Dry-Risers.pdf

Please see page 3 of 4 of the BAFSA document on wet riser pumps and their power supplies. It does not answer your question completely but there are some contact numbers at the end of it. If they don't know they might be able to direct you to someone who does.

Also IFEDA - the Independent Fire Engineering and Distributors Association.

See: ifeda.org

I'd have thought BS9990 has something to say on the matter.

Lastly: High rise wet riser fire systems installation | UK Dry Risers - http://www.ukdryrisers.co.uk/wet-riser-systems.php
Snippets from BS990:2015

Screenshot_20220204-132107_Drive.jpg
Screenshot_20220204-132120_Drive.jpg
Screenshot_20220204-132052_Drive.jpg
 

Reply to Wet Riser Pump back up supplies in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Another one that some of you may be interested in.......... We had a call to remove 4 off blackstone generators from a pumping station in south...
Replies
3
Views
1K
Hi all, quick question - I have to replace a lateral supply cable where the existing one runs through the ceiling of the basement flat and up...
Replies
3
Views
1K
Hi all, I have a regular client who has asked for a battery back up system to be installed at their home. They live in a rural location on a...
Replies
2
Views
1K
I have a customer with a problem of RCD tripping caused by the wet UFH systems. There are 5 UFH areas each with a Wilo Para pump attached. Along...
Replies
29
Views
6K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock