I have been going round in circles with this question. I just cant seem to get an answer remotely close to the options.

Continuity of a ring final circuit has been tested as part of an initial verification of a new primary school. All the socket outlets are connected directly to a ring.

The circuit is 58m long, wired in 4 mm2 live and 1.5 mm2 cpc flat profile cable. The circuit is protected by a 32 A BS EN 60898 Type B circuit breaker.

What is the expected r1 value?

0.27Ω
0.32Ω
0.43Ω
0.52Ω

So I have got the R1+R2 value from the OSG which is 16.71 mΩ/metre
I have multiplied this by the 58 metres equaling 969.18 mΩ
I have times by 4 for the r1+r2 value 3876.72 mΩ
I have then multiplied this by the 4 to 1.5 ratio which is 0.273 equaling 1058.34 mΩ
I then divided by 1000 to get ohms
My answer is 1.05. No where near any of the answers.

What am I doing wrong?

I'd appreciate any help with this. I don't want the direct answer, just how I'm screwing it up.

Thanks in advance.
 
Read the question properly!!! What value is it that you're being asked for?
 
I am being asked for r1. Everything I have looked for takes me to calculating R1+R2. I have read the question multiple times over the last few hours. What am I missing?

Thanks.
 
I am being asked for r1. Everything I have looked for takes me to calculating R1+R2. I have read the question multiple times over the last few hours. What am I missing?

Thanks.
Don't have the OSG to hand but I'm assuming that it should contain the Ohm/m value for 4mm Cu. r1 is that value x length of circuit.
 
r1 is just your first continuity reading, lets say thats the line conductor, aka brown. Then you do your rn aka neutral and lastly your do your r2 aka earth. Its the first readings for continuity you do in the field when testing. So r1 is just the ring continuity brown to brown, which you hope is very close to design if you have remembered how much cable you have used, lol.
rN generally is the same conductor size (not always) but vast majority of the time so it will be similar hopefully within 0.02 ohms.
r2 is the earth continuity which is often, but not always, a smaller sized conductor so yields a higher resistance reading.
The reason we use r1+r2 as a design parameter is because we are trying to design a circuit that will meet the minimum breaker disconnection times which are the ZS values which you will come across. We get that value from r1+r2+ze or zdb . Thats why r1+r2 keeps popping up.
Its good to have a very good idea what your r1, rn and r2 figures should be just before you connect the tester so you can immediately have suspicions if they are way out.
When i am working with an apprentice or mate , to break the tedium we have a guess at the readings and closest does not make the tea :)
Anyway you need to find the resistance /metre for 4sqmm cable you are using , it does not vary that much tbh between all types of cable, its roughly 4.6mOhm per meter.
Good luck
 

Reply to What am I doing wrong with this calculation? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Got my am2 coming up on Tuesday and I know I have to calculate my Zs readings Maybe I’m overthinking this but am not sure if I need to use the Ze...
Replies
17
Views
3K
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Replies
6
Views
2K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock