Outdoor lighting circuit (domestic) without 30mA RCD additional protection, what code would you give it?

I'm leaning toward C2 as (A) outside lights have a habit of filling up with water, and (B) anyone touching it may be in contact with the bare ground.

What are your thoughts?
 
This is probably one of those 2.5s that crop up regularly.

If it's a plastic light, or well outside touching distance I'd almost certainly C3. If it was metal in good condition and with suitable fault protection then I'd C3 too, but if it is looking old or like it was poorly maintained, then that might push it to C2.

BPG4 does say C2 for inadequate IP rating, though doesn't specifically mention anything about outside lights.
 
As above, C3 only. IP rating is another question on the schedule of many questions...
 
Thanks for all your comments.

I often see outdoor lighting in poor shape, mainly due to weathering rather than poor installation, and it's often the cause of RCD tripping, so I consider it 'risky'. Personally, I like to see an RCD protecting it, but I don't write the regs. C3 it is then!
 

Reply to What code? No RCD, outside lights in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
612
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
First : here are 2 x sockets .What code would you give and why ? 3rd pick you can see rear thermal damage on double socket second : Roof...
Replies
32
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock