Discuss What code would you give for the following in the Periodic Inspection Reporting & Certification area at ElectrciansForums.co.uk.

Tags:
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Farmelectrics
    Offline

    Farmelectrics Farmelectrics Electrician's Arms

    Location:
    Wirral
    Business Name:
    Farm electrics
    No schedule in distribution boards what code would you give this previous reports state code 3 I was thinking code 2 but a bit unsure factory environmental
     
  2. Dillb
    Offline

    Dillb Electrician's Arms

    Location:
    Nottingham
    Why are you think of a C2?
     
  3. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    If I were doing EICR on such sites and there is no labelling/schedules I would quote for a survey to identify all circuits and place schedules/labelling before doing the EICR. However you suggest you have access to previous EICR so you could get them to print them out (schedules) and place accordingly. Are the DBs' labelled in terms of identifying the DB themselves throughout the building?
     
    • Agree Agree x 1
  4. Adam W
    Offline

    Adam W Regular EF Member

    Location:
    Bournemouth
    C3 if anything. Provided the circuits are labelled in some way I wouldn't code it at all.
     
    • Like Like x 1
    • Agree Agree x 1
  5. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    Not C2 ...... FI which can also give unsatisfactory

    Previous reports state C3 ... yet nothing has changed ....
     
    • Agree Agree x 1
  6. Risteard
    Offline

    Risteard Respected Member

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    I think it depends on the circumstances. I have come across large installations where there is no labelling where frankly I haven't a clue what is connected to what or where, and what devices things are protected by. I think there is an argument that there is a safety issue - and indeed an issue of maintainability. So I'm not sure that I would agree that a C3 is always appropriate for this.
     
  7. Farmelectrics
    Offline

    Farmelectrics Farmelectrics Electrician's Arms

    Location:
    Wirral
    Business Name:
    Farm electrics
    There is very little labelling hardly anything is marked up even previous eicr states on sheets unidentified ciircut but they've given it as a satisfactory in most boards there's still unidentified circuits so can't understand how it can be given a satisfactory report
     
    • Agree Agree x 1
  8. Risteard
    Offline

    Risteard Respected Member

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    You're absolutely right - it can't possibly be satisfactory when you have no idea where it is going or whether it is safe!
     
  9. Adam W
    Offline

    Adam W Regular EF Member

    Location:
    Bournemouth
    If you can't identify a circuit then you can't test it properly.
    The best course of action would be to get the client to agree to you tracing out the circuits and labelling them then testing them, otherwise you're going to end up with a lot of limitations and further investigation.

    Or rather the client will, on an EICR which won't tell them a lot other than their installation needs work doing to it.
     
  10. essex
    Offline

    essex Forum Mentor

    Location:
    Wiltshire
    It is a C3 all day long for no circuit charts.

    If emergency switching or isolation is required then that would not fall under the Reg for curcuit charts.
     
  11. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    C3 for labelling.

    I've seen someone give a C1 for labelling once, I laugh at him, loudly, for a long time, then called him a w~~~~~....
     
    • Funny Funny x 2
  12. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell.

    Location:
    star command
    FI on the test cert considering that circuit has not been identified.
     
  13. ipf
    Offline

    ipf Forum Mentor

    I got a bad mark off an NICEIC inspector for no schedule in a bleedin' domestic......even though the CU was all labelled up.
    I was half expecting a couple of hours detention or a clip round the earhole.
     
    • Funny Funny x 2
    • Like Like x 1
  14. Paignton pete
    Offline

    Paignton pete Regular EF Member

    Location:
    Over the rainbow
    I like that one Murdoch.
    I agree it doesn't justify a C2 but I'd really want to sort this issue in a larger installation.
    Your F1 does just that.
    Occasionally someone will come up with a good idea on this forum.

    I'm doing a industrial warehouse next week and that issue is also a concern for me. I think I'll use it.

    Cheers
     
  15. mickfred
    Offline

    mickfred Regular EF Member

    Location:
    Liverpool
    Are place got a c1 for no schedule , c1 for using SY c1 for missing RCD testing sticker c1 for no bonding to water mains (when Ch is bonded and incoming is plastic ) he was from the insurance and tried to c1 everything . Don't think he could count past 1
     