You need to be careful when using standard dimmers with ELV transformers, usually no more than 5 per dimmer, depending on maufacturers instructions for the dimmer and the transformer, some makes require a certain kind of dimmer.

Also with regard to GU10 halogens, dimmers should be de-rated by 25 - 50% again depending on make and instructions. You may find that a 500W rated dimmer is only suitable for dimming 250W worth of halogen lighting.

It's worth selecting the correct dimmer form the start as you will only be going back every couple of months to swap it out otherwise.
 

Reply to What Dimmer? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

I have halogen lights in my kitchen under the wall units, there are ten lights altogether bulbs are either 10 watt or 20 watt G4 bulbs ( not sure...
Replies
1
Views
739
I have the typical LED on Dimmer switch. All the lights flicker in my house are very inconsistent times. By let me clarify by saying all the...
Replies
0
Views
897
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
690
Hello folks, So my van got found after being stolen ;D Now I'm installing my own alarm on the van which is triggered when a door is opened. Im...
Replies
4
Views
519
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock