Discuss What EICR code for plastic trunking in escape routes? in the UK Electrical Forum area at ElectriciansForums.net

KevinH

-
Reaction score
62
Hi to all. I'm new and this is my first post.
I'm doing an EICR on a 3 story building split into multiple offices to let.
One thing I noticed is t+e cables in plastic trunking almost throughout (switch/socket drops, across ceilings to lights etc).
Would this be a code 2 or 3? Also would same code be throughout or just in escape routes?
I understand it could potentially be dangerous (causing entanglement when melting/falling etc), but surely an EICR is regarding electrical safety and as far as I can see the installation is electrically safe!
Any views as it would be a massive job to correct.
Surely if its a C2 then most commercial buildings in the country would fail?
Should I just C3 it and suggest landlord gets a fire safety report done?
 
You are inspecting and testing an electrical installation to the current addition of bs 7671 and as such you are checking compliance with regulation 521.11.201 so a code needs applying to this regulation if found non compliant and is a safety concern.

I have applied a C2 to this in the past regarding numerous LV and ELV cables installed above suspended ceilings in escape routes where the cables where mearly supported by twin and earth loops screwed to the existing ceiling, some just screwed into the plasterboard.
If all that lot had come down then yes it’s potentially dangerous in my opinion.
If it’s just the odd piece of trunking without metallic or non combustible supports for the wiring then a C3 at the most if found in escape routes.
 
Last edited:
No code for the plastic trunking. However a definate C3 for cables likely to suffer premature collapse in the event of a fire.
 
It will be interesting to see how this is coded when all wiring in an installation requires protection against premature collapse in a fire and the words escape route is removed, Christ make up your minds!
 
No cables are exposed as all are contained within trunking throughout the installation.
So you guys are saying I give it a C3 ? Im assuming that just applies to the escape routes (stairwells/corridoors etc) as per 521.11.201 and no coding for trunking across ceilings in all rooms.
 
According to my boss, who's really clued up on things like this, it's a C2 because the cables aren't supported by fire resistant fixings; following the normal thought process it would be a C3, ie it used to comply but doesn't any more, but apparently this is an exception because firefighters have died due to it.

Does it have to be a massive job to correct or could you put stainless steel cable ties and bases inside the plastic trunking?
 
To be honest all the guidance written by the so called experts (NICEIC, best practice guide and I’ve read Napits code breakers guide) all do suggest a C2.
Me if it’s a high concentration of cables at risk of collapse then I C2 it.
A picece of yt2 in an escape route with say a twin and earth cable in it on its own C3 as I believe the risk is severely reduced.
As the inspector it lies with you.
 
Thanks guys. Think I will take Ians advice and C2 the 'bulky' concentrations and C3 the odd little ones.
Then if Landlord agrees (and pays) I will secure the worst with stainless ties and bases inside the trunking as Adam suggests.
Cheers!
 
Thanks guys. Think I will take Ians advice and C2 the 'bulky' concentrations and C3 the odd little ones.
Then if Landlord agrees (and pays) I will secure the worst with stainless ties and bases inside the trunking as Adam suggests.
Cheers!

It’s irrelevent what the landlord thinks..... you are doing an EICR and any remedial work is up to them ........ the landlord is under no obligation to get anything done.
 
We were once told to fall withing fire regs the cable within the trunking had to be supported with something such as a butterfly clip every 300 or 900mm i cant remember what distance now. Is this correct?
 
Problem with this new requirement, is that the danger existed before the Regulation was introduced.
It now not only presents a danger but is also a non-compliance.
Surely you could say that about any changes to the regs?
For example previously RCD protection could be omitted if the installation was under the supervision of a skilled or instructed person, but since that was abused and disallowed the same circuit which previously didn't require RCD protection would now not be compliant.

The requirement for fire resistant supports doesn't have to be expensive or intrusive, as I mentioned earlier it could simply involve taking out a few screws and adding metal cable tie bases and cable ties. It doesn't even have to be all the way along, just every metre or so to keep the cables out of the way in the event of a fire.
 
There’s never been an exception to omit RCD protection to circuits.
My point is, that having cables anywhere (not just escape routes) which can fall down and entangle fire fighters has always been a dangerous situation warranting a code C2.
Just because there is now a specific requirement does not mean it should only warrant a code C3.
 
Last edited by a moderator:
There’s never been an exception to omit RCD protection to circuits.
That was just the first example I could think of, but there has - as I said if the installation was under the supervision of skilled and instructed operatives, dedicated circuits for specific items of equipment, if a risk assessment was attached to the certificate, there may have been others.
It seems the 18th edition is largely about removing these 'loopholes'.
 
I think a C2 is too strong personally. But it is what the guidance notes suggest.

If the ceiling is fire boarded then a C3 surely.
 
There was an exception to omit RCD protection for cables concealed in walls if the installation was under the control of a skilled or instructed person.
There was also an exception to omit RCD protection for socket-outlets if their use by ordinary persons was supervised by a skilled or instructed person.
 
C2? rollox, there would be hundreds of millions of pounds worth of urgent work required in hundreds of thousands of properties, C3 at best, it was perfectly safe before they updated the Regs lol, the world wasn't going to end then.
 
As usual, ill thought out regs, poor communication and inconsistent application of codes..............................

Should we be surprised?
 
We had a seminar today from one of the surveyors, which was largely about fire safety.
Apparently (unlike BS7671) fire regulations are retrospective, hence lack of fire resistant supports being a C2 and not a C3. I suppose the logic behind this is the best person to rectify it would be an electrician.
 

Reply to What EICR code for plastic trunking in escape routes? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
669
Hi all, Been asked to do EICR on thatched property for insurance purposes, however they will want all C3 codes rectified. Haven't seen it yet but...
Replies
10
Views
1K
Morning, Company had an external contractor coming in to complete an EICR recently. They have gave us the report with a C2 for holes in trunking...
Replies
22
Views
3K
Hi. Looked at a job this morning for remedial work on an EICR. The inspection has noted the plastic consumer unit within the hallway cupboard and...
Replies
7
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
740

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock