On a Eicr on agreed limations of iinpections what do you normally put
And what percentage do you test at..
And what percentage do you test at..
Discuss What limations do you put on a Eicr. in the UK Electrical Forum area at ElectriciansForums.net
so what do write on your sheet.Depends on installation & agreed limitations
Usually DB 100% 70% of final circuits 50% of accessories on these circuits.
Operational limitations may also exist ie: Isolation of DB/CU & circuits not possible during this EICR
YEs i should have mentioned as a one man band I won't move any heavy stuff like those big American fridge / freezers and I won't lift down any wall mounted flat TVs etc. This is more a manual handling limitation / coverning my own ---.my agreed limitations and operations limitations .
no inspections to the switches to a point and outlets in the kitchen with a limited working space .
i.e.where access to a point is blocked by heavy /bulk appliances and where the point concealed by fixed furniture or alike .
limited insulation Resistance testing to the circuits supplying luminaires and other connected equipment having vulnerable equipment.
What I stated on my postso what do write on your sheet.
Wouldn't really agree. It shouldn't be necessary (and indeed may be undesirable) to remove every faceplate for inspection - even in a domestic property. There is a risk of introducing faults doing this. Around 20% of accessories should be perfectly adequate.When doing domestics I try to avoid too mant limitations , if I can get to every accessory I will do my best to do so.
I always go in the loft ( i know plent sparks who don't ) and as part of my day I will do all out buildings and any garden wiring etc again I know sparks who just say outdoor wiring unchecked for example.
My honest opinion is if you can't do an Eicr fully in domestics then there is no point.
Commercial / Industrial is a totally different ball game