Depends on installation & agreed limitations
Usually DB 100% 70% of final circuits 50% of accessories on these circuits.
Operational limitations may also exist ie: Isolation of DB/CU & circuits not possible during this EICR
 
When doing domestics I try to avoid too mant limitations , if I can get to every accessory I will do my best to do so.
I always go in the loft ( i know plent sparks who don't ) and as part of my day I will do all out buildings and any garden wiring etc again I know sparks who just say outdoor wiring unchecked for example.
My honest opinion is if you can't do an Eicr fully in domestics then there is no point.

Commercial / Industrial is a totally different ball game
 
my agreed limitations and operations limitations .
no inspections to the switches to a point and outlets in the kitchen with a limited working space .
i.e.where access to a point is blocked by heavy /bulk appliances and where the point concealed by fixed furniture or alike .
limited insulation Resistance testing to the circuits supplying luminaires and other connected equipment having vulnerable equipment.
 
my agreed limitations and operations limitations .
no inspections to the switches to a point and outlets in the kitchen with a limited working space .
i.e.where access to a point is blocked by heavy /bulk appliances and where the point concealed by fixed furniture or alike .
limited insulation Resistance testing to the circuits supplying luminaires and other connected equipment having vulnerable equipment.
YEs i should have mentioned as a one man band I won't move any heavy stuff like those big American fridge / freezers and I won't lift down any wall mounted flat TVs etc. This is more a manual handling limitation / coverning my own ---.
 
When doing domestics I try to avoid too mant limitations , if I can get to every accessory I will do my best to do so.
I always go in the loft ( i know plent sparks who don't ) and as part of my day I will do all out buildings and any garden wiring etc again I know sparks who just say outdoor wiring unchecked for example.
My honest opinion is if you can't do an Eicr fully in domestics then there is no point.

Commercial / Industrial is a totally different ball game
Wouldn't really agree. It shouldn't be necessary (and indeed may be undesirable) to remove every faceplate for inspection - even in a domestic property. There is a risk of introducing faults doing this. Around 20% of accessories should be perfectly adequate.
But the short answer as to what to include in the agreed limitations is whatever limitations have been agreed with the Client.
 
On a Domestic 100% of circuits.
minimum 10% of accessories per circuit opened as a starting point, increased at the faintest whiff of something not right at either the opened accessory or the installation in general. 100% of accessories risks unnecessary damage to the decor and increases the risk of introducing a fault. Practically on a circuit I would open the usual suspects for dodginess first and take it from there.
Things like shower circuits I would open the isolator and the unit.
Visual of all accessible faceplates and accessories.
Testing 100% at board, global IR test. Testing at multiple points of lighting circuits if end point isn't obvious.
My take on it is that the IET have a fairly good idea of what is needed on an EICR and that sampled inspections are the way forward.

Each installation is different some can be rattled through very quickly, others raise flags and need significantly more time.
 
IMO regarding these reports, its all about observation with what you are seeing with your eyes ( very good tool) If the installation on the whole is looking good any sockets you take off, light switches, drop any light fittings etc all fine then no need to take every single one off. Its called sampling
However if what your seeing is absolutely awful the more you are going to investigate and drill down on.
Its going to be 100% at the CU because your testing from there.
Who calculates R1 R2 off r1 r2 on RFC or does anybody do fig 8 and go round to every socket ? (just curious)
 

Reply to What limations do you put on a Eicr. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I need an EICR done on a house I rent out in Reading, England - 4-bed detached built in early 1980s. Would ideally like someone from this forum...
Replies
2
Views
467
Just come across this on the web from a so called expert company: Most common items that fail an EICR, What Landlords need to know before booking...
Replies
4
Views
569
Hi all. Just trying to get a feel for what everyone is charging for a commercial or industrial EICR with or without the previous report. Seems to...
Replies
4
Views
670
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Replies
20
Views
671

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock