Good evening everyone. Went to change my parents CU for them yesterday, I've never looked at the supply before, even when I lived there. I looked at the supply and there is no main earth? The only bonding there is. Is 10mm to the gas. First thought the gas was being used as earth but with connected ze 1.27 and with it disconnected 1.24 so this obviously isn't the case. They live in Norwich 1950's house along the biggest road through Norwich.

Does the system require me to call dno for PME upgrade? I remember about two years ago looking the next doors for a rewire and am sure they where TN-C-S .

What do you guys recommend?

Thanks!
 
old cast iron cutout then here.....just your luck as DNO`s are changing em free of charge....so should be able to PME your supply at the same time....just leave a length of 16mm earth for em ready....and they should connect it into the neutral link in the new cutout when they come to fit it....
 
old cast iron cutout then here.....just your luck as DNO`s are changing em free of charge....so should be able to PME your supply at the same time....just leave a length of 16mm earth for em ready....and they should connect it into the neutral link in the new cutout when they come to fit it....

That's great thanks for the help. So I can change board and test then retest when dno have done? Sorry for sounding imcompetant but never come across this it
 

Reply to What's going on Here? in the Australia area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
582
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi all, After months of waiting, the fused neutral cut-out at my parents house has been replaced but I am concerned about the main earth. I...
Replies
6
Views
3K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I'm going to start some construction projects at my own gaff soon, including sorting out some better outdoor supplies. Currently have a 32a...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock