- Reaction score
- 12
Called to a property which has just been sold to do an EICR
The sockets down stairs including the kitchen were on a 16a 2.5 radial the issue being the Zs for the first couple of sockets were about average readings but the last few and the sockets in the kitchen went from 0.90 ohms to 1.19 ohms. Personally I wouldn’t put a kitchen on a radial but that’s just my preference. But why the higher than normal results could it be a case of more than one spur from a socket That’s giving me high readings also 16a is just not cutting it. The property had an EICR done a few months ago but no concern over higher readings on socket radial for the down stairs sockets including the kitchen being on a 16a 2.5 cable your comments would be appreciated
The sockets down stairs including the kitchen were on a 16a 2.5 radial the issue being the Zs for the first couple of sockets were about average readings but the last few and the sockets in the kitchen went from 0.90 ohms to 1.19 ohms. Personally I wouldn’t put a kitchen on a radial but that’s just my preference. But why the higher than normal results could it be a case of more than one spur from a socket That’s giving me high readings also 16a is just not cutting it. The property had an EICR done a few months ago but no concern over higher readings on socket radial for the down stairs sockets including the kitchen being on a 16a 2.5 cable your comments would be appreciated