As a trainee can I ask why the banjo is on the outside of the Wiska box. I understand that the earthing of the SWA must be maintained but would having the banjo outside mean you need to drill through the IP66 box to connect to earth and by doing that are you not compromising the IP rating? I understand the earth locknut is inside the box so what function does the banjo have when it's outside the box and not connected to anything?
banjo.jpg
 
It tends to act as a load spreading washer, allowing the nut to be tighter without the gland digging into the plastic of the box.
IP23 is arguably the minimum for a box mounted where that one is, so a little compromising of the IP66 rating is acceptable.
 
As a trainee can I ask why the banjo is on the outside of the Wiska box. I understand that the earthing of the SWA must be maintained but would having the banjo outside mean you need to drill through the IP66 box to connect to earth and by doing that are you not compromising the IP rating? I understand the earth locknut is inside the box so what function does the banjo have when it's outside the box and not connected to anything?
View attachment 110348
In that configuration, you would have to drill a hole and nut and bolt a fly lead to earth the armour.
The easiest way is to use an earth plate.
 
In that configuration, you would have to drill a hole and nut and bolt a fly lead to earth the armour.
The easiest way is to use an earth plate.
Thanks for taking the time to reply. I found this on an electricians youTube video and can't understand why he didn't use an pirana nut or earth plate like this?
pirana.jpg
 
In that configuration, you would have to drill a hole and nut and bolt a fly lead to earth the armour.
The easiest way is to use an earth plate.
Thanks for taking the time to reply. What I don't understand is why he put the banjo outside the Wiska box?
 
Thanks for taking the time to reply. What I don't understand is why he put the banjo outside the Wiska box?
The banjo won't fit inside the Wiska, the inside wall is not flat. Normally I'd fit an earth bar inside that has a profile machined to fit.

See post #5. There are different earth bars available to suit different Wiska sizes, the '308 is the most common size.
 
The banjo won't fit inside the Wiska, the inside wall is not flat. Normally I'd fit an earth bar inside that has a profile machined to fit.

See post #5. There are different earth bars available to suit different Wiska sizes, the '308 is the most common size.
Thanks very much to you and all who replied - that's answred it. I know what you mean by the Earth Clamp Bar for SWA.
WKEC308.jpg
 
Thanks very much to you and all who replied - that's answred it. I know what you mean by the Earth Clamp Bar for SWA.
View attachment 110366
You’ll never get a hammer and chisel in there to tighten it up…..
Sorry, wrong thread. 😂


There may be a situation where that particular banjo isn’t required at all. Whether it comes in the pack or not…. It isn’t always required.
 

Reply to What's the Banjo doing? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K
Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
950
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
Hello, I am burying a fiber optic cable so I have internet in my garage. I have purchased the following flexible conduit to run the fiber optic...
Replies
2
Views
871
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
978

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top