M
Maxstone89
I think i know but want to make sure
Discuss Whats this mean on a rcd test in the UK Electrical Forum area at ElectriciansForums.net
could be that. could also be that OP had the meter set to a dead test function.
It was not a new install it, and i came to the conclusion that when i unplugged everything using power eg modem tv ect the test worked.
What, it is aloud to be done at a socket actually
To the best of my knowledge an RCD test should be carried out with the outgoing conductors disconnected.
http://electrical.------.org/wiring-matters/15/insp-test-rcd.cfm?type=pdfWhat evidence can you find to say it has to be done your way?
6.12.10 just states use a suitable rcd tester , doesn't say how,
What evidence can you find to say it has to be done your way?
I understand your hypothesis for testing an RCD (i.e. just testing the RCD only), but how do you do that in the case of a dual RCD CU, without having to deconstruct the bus bars etc? You would also be carrying out an unnecessary live test, with the CU cover removed, when the test can be carried out at a socket without exposure to live parts, unless I'm not understanding you correctly. Why would manufacturers supply such test leads?Then you are not carrying out the test correctly!
RCD tests should be carried out at the outgoing terminals of the RCD with the outgoing conductors disconnected.
Perhaps you should revise your test procedures a bit before carrying out any more testing.
I understand your hypothesis for testing an RCD (i.e. just testing the RCD only), but how do you do that in the case of a dual RCD CU, without having to deconstruct the bus bars etc? You would also be carrying out an unnecessary live test, with the CU cover removed, when the test can be carried out at a socket without exposure to live parts, unless I'm not understanding you correctly. Why would manufacturers supply such test leads?
Yes it does, the bit where it said "the test should be conducted at........."I know , I was just showing you where it was written.
Thanks for that Glenn. I think I just did though but just in case....Trev is always welcome and it is good to see you back matey I and a lot of others have missed you now can you put these silly sods straight about testing rcd's in the way only you can:rofl:
However, if there is no load you can test at the RCD without disconnecting the circuit.
Yes it does, the bit where it said "the test should be conducted at........."
Nice to see somethings never change on here guys.
Not a bloody clue Steve, how the hell are you?Who are you?
NICEIC ALLOW rcd test to be done at the socket.
on my yearly checkup, id put in a new socket radial circuit, he asked me some questions and then to show him how i carried out all my testing, hes said nothing when i showed him an rcd test via the socket.