I think H&S and supporting statutes have something to say on this. Strictly speaking getting up a ladder to test lights is a no no in some commercial places I have been in. And opening a CU is working on something live which we should not be doing if there is a safer way to work i.e. at a socket or light switch. Therefore not at the CU with cover off then?
 
suppose you test the RCD at CU with circuits dissed. it passes with good readings. installation is then re-energised, cert. supplied, next job. however 1 circuit has a nasty N-E fault which inhibits the RCD from working. customer is electrocuted. if test was carried out at a socket, the problem would have been seen and rectified. so I'm with spin on this issue.
 
suppose you test the RCD at CU with circuits dissed. it passes with good readings. installation is then re-energised, cert. supplied, next job. however 1 circuit has a nasty N-E fault which inhibits the RCD from working. customer is electrocuted. if test was carried out at a socket, the problem would have been seen and rectified. so I'm with spin on this issue.
I'm with Spin and Tel
 
It’s all about why you are testing the RCD/RCBO.
If you are testing it just to see whether it works, then yes test at the most convenient point.
If you are testing to prove it provides additional protection, then test it at the point where the additional protection is required.

Not aware anyone is getting aggressive about it.
Incorrect premise.
 
suppose you test the RCD at CU with circuits dissed. it passes with good readings. installation is then re-energised, cert. supplied, next job. however 1 circuit has a nasty N-E fault which inhibits the RCD from working. customer is electrocuted. if test was carried out at a socket, the problem would have been seen and rectified. so I'm with spin on this issue.
Your insulation tests would have discovered this.
 
Your insulation tests would have discovered this.
you'd think so, but IR testing with modern digital testers can be hit and miss. had several cases of trapped L conductors showing >299Meg. on test but tripping MCB when energised. also had a couple of N-E fault stopping RCDs working . tested fine, >200Meg. .as a last resort on one of the latter, i used old wind up megger. that showed 15K ohms. think it's the fact that the old wind up jobbies can push out higher current. . moral here is don't mock the oldies. (you listening pete? old school beats the new tech.... hands down).
 
I think H&S and supporting statutes have something to say on this. Strictly speaking getting up a ladder to test lights is a no no in some commercial places I have been in. And opening a CU is working on something live which we should not be doing if there is a safer way to work i.e. at a socket or light switch. Therefore not at the CU with cover off then?
I'm with Vortigern on this.
I think this should be the definitive answer.
 
you'd think so, but IR testing with modern digital testers can be hit and miss. had several cases of trapped L conductors showing >299Meg. on test but tripping MCB when energised. also had a couple of N-E fault stopping RCDs working . tested fine, >200Meg. .as a last resort on one of the latter, i used old wind up megger. that showed 15K ohms. think it's the fact that the old wind up jobbies can push out higher current. . moral here is don't mock the oldies. (you listening pete? old school beats the new tech.... hands down).
Agree
 
I just press the test button, am i doing something wrong then?:rolleyes:

I think when AFDD's, RCD's and MCB's are combined in one unit - that's all we'll be able to do. AFRCBO's? and then throw in an SPD somewhere.
 
I think the point that keeps getting overlooked is that (barring Tel's odd insulation fault thing) a typical circuit that passes the dead tests is not going to make any difference to whether the tester performs a valid test on the RCD, nor affect whether a functioning RCD will successfully provide additional protection. A long, highly capacitive circuit will add some leakage current and may affect the result, making the RCD look more sensitive than it is in itself, although without impairing the protection because it genuinely will trip at the measured lower current when in use on that circuit. But that only impacts whether it is worth disconnecting the circuit, not where to attach the tester leads while the circuit remains connected. Leaving loads connected is a different matter and can significantly affect the results.

An analogy would be to argue that since windscreen wipers are used to wipe rain off, the only valid test for the MOT would be to put the car outside and wait for it to rain, and see if the wipers removed it. Overlooking the fact that they remove water from any source with similar efficiency, just as an RCD responds to a particular injection test current with similar efficiency regardless of where on the circuit it is injected.

The thing about RCDs that don't respond to a test at the screw terminals, is that they use the circuit conductor, as it passes through the plastic housing into the terminal, as part of the balance transformer. It has nothing to do with the length of cable etc, only where the test probe current physically enters the device. It must go through the cable hole, not the screw hole.
 
So a device that is;-

Arc fault detection
Residual current
Surge protection
Equipment

Sounds like a bit of a pain in the A.R.S.E

I tried so hard to get that to work but I had a couple of beers... well done. Exactly
 
i used old wind up megger.
I have an old "hold the button and what the needle does" IR & resistance tester that dad picked up when it was being ----ed out at work. In my rental flat, I can use that to test the whole installation for IR as it will provide voltage for long enough to charge caoacitance (eg in PIR lights that are inconvenient to disconnect) - but MFT simply doesn't apply voltage for long enough and gives random results.
IMO that's far preferable to all the disturbance that would be caused by disconnecting all the circuits from their RCBOs. At some point you have to consider if the testing is introducing more risk than it might be mitigating ? And given the terminal design (I'm thinking of those long RCBOs where the L&N are one above the other so one is deeply recessed and impossible to visually inspect) of some devices, disconnecting them is creating a risk that isn't warranted IMO.
 

Reply to When testing a circuit protected by RCBO, do you test at the DB or furtherst point in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
694
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
854
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
896
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
518
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock