Discuss Which box to use please in the UK Electrical Forum area at ElectriciansForums.net

John41

-
Reaction score
0
Having a slight argument with a supposed electrician

Now I always thought when flush fitting an internal double socket to to an external wall. It's safer to use the metal boxes

Now the guys is going to use a plastic box (I actually thought these were for stud walls.

I asked if it would be safer just to surface mount and he went through me saying metal boxes are rubbish they rust. (Weird how they've been used for alot of years)

I thought it would be best to ask here

Thanks in advance
 
If its a masonry wall then its normal practice to fit a metal knock out box. The box wont rust unless you have no DPC.
Dry lining box for stud walls or if flat profile sockets are being fitted a noggin and knock out box.
 
Are you saying he sinks normal plastic back boxes into masonry walls?
 
Thank you, and yeah it's masonry. Not sure about DPC

I'll ask him to use metal as it's already cost enough for this kitchen, don't want anything going wrong

John L
 
I would use a metal back box but for a second here let’s indulge discussion as to why plastic couldn’t be used. The early back boxes were metal because the metal conduit joined to it making the only earthing connection - single wire runs of what was [back then] live and neutral. That’s why the earth terminal is in the back, to bring it to the socket output (because there wasn’t a wire). It’s not the 1950’s - why not plastic back boxes?
 
Are we talking plastic drylining boxes with the adjustable lugs, fixed into brick... or is there a plastic version of the regular metal backboxes?
 
I would use a metal back box but for a second here let’s indulge discussion as to why plastic couldn’t be used. The early back boxes were metal because the metal conduit joined to it making the only earthing connection - single wire runs of what was [back then] live and neutral. That’s why the earth terminal is in the back, to bring it to the socket output (because there wasn’t a wire). It’s not the 1950’s - why not plastic back boxes?

With early conduit systems in domestic installs I have mostly seen wooden backboxes, not metal.

I have only ever seen a few metal boxes rusted to the point of it being an issue. Perhaps the location of the OP has a bearing on this ? Is the installer acting on experience ?
 
I would use a metal back box but for a second here let’s indulge discussion as to why plastic couldn’t be used. The early back boxes were metal because the metal conduit joined to it making the only earthing connection - single wire runs of what was [back then] live and neutral. That’s why the earth terminal is in the back, to bring it to the socket output (because there wasn’t a wire). It’s not the 1950’s - why not plastic back boxes?

At one time plastic 16mm single flush boxes were available for light switches in installations with no cpc.

The biggest reason not to use plastic flush boxes now is that either don't exist or are extremely rare if they do. A normal surface pattress is too big and too brittle to work as a flush box.
 
If an external wall of dubious quality (early white block or simply carp construction materials has been dot and dabbed with plasterboard I would probably use plastic back boxes as it would probably be a better fixing. Wouldn't use them routinely over metal back boxes.
 
Metal boxes are common practice because that's what we are used to but realistically there is no reason why he can't use a plastic box there is nothing wrong with it
 
Metal boxes are common practice because that's what we are used to but realistically there is no reason why he can't use a plastic box there is nothing wrong with it

It will be hard to get a neat finish around whatever is fitted to the box due to the plastic boxes available being the same size as the accessories as they are intended for surface mount use.
 
It will be hard to get a neat finish around whatever is fitted to the box due to the plastic boxes available being the same size as the accessories as they are intended for surface mount use.
In any case apart from the odd light switch I don't think I've ever seen it done
 
Certainly sounds unorthodox. Not necessarily wrong though, but I do wonder why you'd do it.
Are the walls drylined on a metal furring system or are they just standard plaster onto blockwork?
 
Hi John - All the plastic back boxes I've seen are either surface mount or designed to lock into the plasterboard of a stud wall. Can you post a pic of what he has done?
 
If it's damp enough for a galv. steel box to rust when sunk in a wall, then it's too damp for any flush box in the wall! Socket will be affected by damp which will show up on future IR readings.
Either fit surface boxes, or you could try the method I've used 100's of times over the years - dig an oval shaped hole out of the wall, about ten times the volume of the metal box, rough render the inside of the hole, coat the render with a couple of coats of tanking compound, suspend the box in its exact place with a piece of batten fixed across the front of the box and fixed to the wall either side, and then fill in the hole around the box with mortar.
 

Reply to Which box to use please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
750
An odd question granted but bear with me. I've got to extend a radial circuit in a community centre to fit a new hand dryer in the toilets, but I...
Replies
15
Views
3K
Hey everyone, I'm trying to understand how to fit a metallic back box on a stud wall. Should it be fixed to a stud (on one of the sides) or is it...
Replies
20
Views
5K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
651
Hi, New to the forum. I have two very specific questions, for the setup below. Setup details: Currently I have a setup with an outlet used for...
Replies
6
Views
586

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock