Which RCD to use for EV charging point?

Discuss Which RCD to use for EV charging point? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Reaction score
5,659
I don't fit EV charging points as I am not OLEV registered. However, I am fitting a Tesla EV charger soon for a friend as I owe him a favour.

The Tesla spec asks for a Type B RCD or Type A-EV RCD.

Looking at Regulation 722.531.2.101 this sates the same as above.

The regulation states a Type A RCD AND appropriate equipment that provides disconnection of the supply in the case of DC fault current above 6mA.

Is this 'equipment' located in specific Type A RCD, or in certain EVCP's, or a seperate piece of equipment?

The tesla wall charger spec says it does not measure DC current leaking.

It sounds easier just to go for a type B RCD but it is difficult to locate one, could any EVCP installers send a link?

Thanks :)
 
Just order one from wholesalers, Doepke appear to be the most used.
BTW TP ones arnt cheap >£400 ... eek
Doepke have good technical documents as well.

True it is not cheap, but then having 3-phase domestic supply and buying a Tesla car is not usually done on a tight budget!
[automerge]1600016647[/automerge]
Doepke also do RCBO with 'type B' DC sensitive trip as well.
 
Doepke have good technical documents as well.

True it is not cheap, but then having 3-phase domestic supply and buying a Tesla car is not usually done on a tight budget!
[automerge]1600016647[/automerge]
Doepke also do RCBO with 'type B' DC sensitive trip as well.
Could I ask why you've mentioned 3 phase supply @pc1966 ? My friends supply is single phase. Are the tesla chargers only compatible with 3 phase, I wouldn't have thought so?
 
The DC RCD is in the charger usually. You'll also need specific test equipment to carry out the full compliment of tests and ensure it all works as it should.

Look on the tube, I think smug Jordan has done a video on fitting a Tesla charger
 
The DC RCD is in the charger usually. You'll also need specific test equipment to carry out the full compliment of tests and ensure it all works as it should.

Look on the tube, I think smug Jordan has done a video on fitting a Tesla charger
The tesla spec does say that the tesla charger does not detect DC leakage.
 
The tesla spec does say that the tesla charger does not detect DC leakage.
Interesting, one Tesla charger manual I looked at last year seemed to have all the required RCD protection built into the charger, the fault lights would even display exactly the fault condition that caused it to shut down. I don't get involved with EV chargers as it seems like a pain to meet all the installation requirements.
 
I have found this one, but it is chint which I dislike:

I have also found this

but I am not sure if it is single phase. I never work with 3 phase so do not recognise if the RCD is for 3 phase (as it is rather wide!)
 
I have found this one, but it is chint which I dislike:

I have also found this

but I am not sure if it is single phase. I never work with 3 phase so do not recognise if the RCD is for 3 phase (as it is rather wide!)
It's single phase. They used to do a three phase version with one phase wired through it but I think they got a single phase two pole version later. Either way it doesn't matter - it is configured for single phase. I haven't been able to beat them on price. (I have a trade account with them so pay less than the quoted prices also.)
[automerge]1600022373[/automerge]
Incidentally I would remove the spare circuit breaker and blank it off. In spite of what it suggests it would be non-compliant to connect anything to the other circuit breaker as the RCD (which must interrupt all live conductors) must be dedicated solely to one EVSE and nothing else.
 
Last edited:
Interesting. I've never come across an RCBO with Type B RCD characteristics - only RCCBs. Do you have a link to these devices?
I don't know if they are offered in the UK/ROI but this is what I remember seeing:
 
This one looks perfect :)

As suggested I shall just blank off the spare way and explain to my friend that it is not to be used.
 
I fit loads of chargers. You don't need to be olev approved to install them. Only if you want to offer the £350 grant do you need that. It's just changed, now we can fit any olev approved charger not just ones we have manufacturers approval for.
If the charger has in built 6maDC protection then you need a Type A RCD or RCBO. Can't recall if the tesla unit has this?
Cheapest source of type a rcbos is ironically Rolec. The new RCBOs seem better than the old blue ones which melted!
Not a fan of the tesla wall charger. Find it quite poorly built and flimsy. Also has a huge hole in bottom you need a 32mm gland for as the supplied plugs are often poorly made and undersized. On the positive you can link 4 together to share load easily.
Best options for easy install is the zappi. It only needs a MCB upfront as all the RCD and DC monitoring and earth monitoring is in the charger and needs no earth rod.
[automerge]1600028112[/automerge]
This one looks perfect :)

As suggested I shall just blank off the spare way and explain to my friend that it is not to be used.
Have used these and very good. Perfect for the job.
 
I fit loads of chargers. You don't need to be olev approved to install them. Only if you want to offer the £350 grant do you need that. It's just changed, now we can fit any olev approved charger not just ones we have manufacturers approval for.
If the charger has in built 6maDC protection then you need a Type A RCD or RCBO. Can't recall if the tesla unit has this?
Cheapest source of type a rcbos is ironically Rolec. The new RCBOs seem better than the old blue ones which melted!
Not a fan of the tesla wall charger. Find it quite poorly built and flimsy. Also has a huge hole in bottom you need a 32mm gland for as the supplied plugs are often poorly made and undersized. On the positive you can link 4 together to share load easily.
Best options for easy install is the zappi. It only needs a MCB upfront as all the RCD and DC monitoring and earth monitoring is in the charger and needs no earth rod.
[automerge]1600028112[/automerge]

Have used these and very good. Perfect for the job.
Thanks for all, it was very useful :)
With regards the unit I have linked in my last post, the RCD takes up 4 modules and has 415V written on it. It states single phase but looks like 3 phase. is it single phase and if so why all the extra positions for conductors (as if it was 3 phase)?
 
Thanks for all, it was very useful :)
With regards the unit I have linked in my last post, the RCD takes up 4 modules and has 415V written on it. It states single phase but looks like 3 phase. is it single phase and if so why all the extra positions for conductors (as if it was 3 phase)?
Not sure why but some type b RCDs are 3 module. That supplier do good double pole RCDs. Give them a call.
 

Reply to Which RCD to use for EV charging point? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock